Choosing LVCTs for PM5320R meters

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
swil
Commander
Commander
0 Likes
2
544

Choosing LVCTs for PM5320R meters

Hi,

 

The link for the PM5320R LVCT meter installation guide suggests that solid core 3-in-1 Quick Click LVCT range can connect to these power meters (E.g. METSECTV45025 for 45mm centres, 250A:0.333V).   

 

Are there any split core LVCT options available. What is actually required is a split core LVCT for 2000A : 0.333V ratio.

 

I have a list of split core LVCTs for only iEM3400, EM3500, BCPM and EM4800 meters, and Rogowski coils for iEM3500 series:split core CTs and Rogowski coils.JPGWhat similar options are available that are compatible with the PM5320R ?

 

Thank you for any assistance.

 

Tags (1)

Accepted Solutions
Charles_Murison
Picard Picard
Picard
0 Likes
1
541

Re: Choosing LVCTs for PM5320R meters

Hello @swil ,

 

The catelog page for the PM5000 series has a note on the bottom "PM5310R and PM5320R must be used with Schneider Electric 3-in1 LVCTs (ref numbers beginning METSECTVxxxxx)" https://download.schneider-electric.com/files?p_enDocType=Catalog&p_File_Name=PLSED309005EN_Web.pdf&... page 96. Same document also has page 103 with 0.333V 3-in-1 CTs with RJ45 for PM53x0R. 

 

I do not believe the LVCTs mentioned in your post have the RJ45 connection at the end

 

Regards,

Charles. 

 

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
2 Replies 2
Charles_Murison
Picard Picard
Picard
0 Likes
1
542

Re: Choosing LVCTs for PM5320R meters

Hello @swil ,

 

The catelog page for the PM5000 series has a note on the bottom "PM5310R and PM5320R must be used with Schneider Electric 3-in1 LVCTs (ref numbers beginning METSECTVxxxxx)" https://download.schneider-electric.com/files?p_enDocType=Catalog&p_File_Name=PLSED309005EN_Web.pdf&... page 96. Same document also has page 103 with 0.333V 3-in-1 CTs with RJ45 for PM53x0R. 

 

I do not believe the LVCTs mentioned in your post have the RJ45 connection at the end

 

Regards,

Charles. 

 

L4 Prime for Advanced metering and Utilities
Tags (1)
swil
Commander
Commander
0 Likes
0
537

Re: Choosing LVCTs for PM5320R meters

Thanks Charles. I didn't think that question through. 

 

The LVCT meter won't be used in this case because the solid core LVCTs recommended in the PM5320R (LVCT meter) installation guide do not meet requirements.

Tags (1)