Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Choosing LVCTs for PM5320R meters

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Choosing LVCTs for PM5320R meters
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
581
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
swil
swil
Mentor

Posted: ‎2020-11-09 12:56 AM

0 Likes
2
2138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-11-09 12:56 AM

Choosing LVCTs for PM5320R meters

Hi,

 

The link for the PM5320R LVCT meter installation guide suggests that solid core 3-in-1 Quick Click LVCT range can connect to these power meters (E.g. METSECTV45025 for 45mm centres, 250A:0.333V).   

 

Are there any split core LVCT options available. What is actually required is a split core LVCT for 2000A : 0.333V ratio.

 

I have a list of split core LVCTs for only iEM3400, EM3500, BCPM and EM4800 meters, and Rogowski coils for iEM3500 series:split core CTs and Rogowski coils.JPGWhat similar options are available that are compatible with the PM5320R ?

 

Thank you for any assistance.

 

Labels
  • Labels:
  • PM Guidebooks
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-11-09 09:11 AM

0 Likes
1
2134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-11-09 09:11 AM

Hello @swil ,

 

The catelog page for the PM5000 series has a note on the bottom "PM5310R and PM5320R must be used with Schneider Electric 3-in1 LVCTs (ref numbers beginning METSECTVxxxxx)" https://download.schneider-electric.com/files?p_enDocType=Catalog&p_File_Name=PLSED309005EN_Web.pdf&... page 96. Same document also has page 103 with 0.333V 3-in-1 CTs with RJ45 for PM53x0R. 

 

I do not believe the LVCTs mentioned in your post have the RJ45 connection at the end

 

Regards,

Charles. 

 

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 2
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-11-09 09:11 AM

0 Likes
1
2134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-11-09 09:11 AM

Hello @swil ,

 

The catelog page for the PM5000 series has a note on the bottom "PM5310R and PM5320R must be used with Schneider Electric 3-in1 LVCTs (ref numbers beginning METSECTVxxxxx)" https://download.schneider-electric.com/files?p_enDocType=Catalog&p_File_Name=PLSED309005EN_Web.pdf&... page 96. Same document also has page 103 with 0.333V 3-in-1 CTs with RJ45 for PM53x0R. 

 

I do not believe the LVCTs mentioned in your post have the RJ45 connection at the end

 

Regards,

Charles. 

 

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
swil
swil
Mentor

Posted: ‎2020-11-09 10:17 AM

0 Likes
0
2130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-11-09 10:17 AM

Thanks Charles. I didn't think that question through. 

 

The LVCT meter won't be used in this case because the solid core LVCTs recommended in the PM5320R (LVCT meter) installation guide do not meet requirements.

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.