Hi,
The link for the PM5320R LVCT meter installation guide suggests that solid core 3-in-1 Quick Click LVCT range can connect to these power meters (E.g. METSECTV45025 for 45mm centres, 250A:0.333V).
Are there any split core LVCT options available. What is actually required is a split core LVCT for 2000A : 0.333V ratio.
I have a list of split core LVCTs for only iEM3400, EM3500, BCPM and EM4800 meters, and Rogowski coils for iEM3500 series:What similar options are available that are compatible with the PM5320R ?
Thank you for any assistance.
Link copied. Please paste this link to share this article on your social media post.
Hello @swil ,
The catelog page for the PM5000 series has a note on the bottom "PM5310R and PM5320R must be used with Schneider Electric 3-in1 LVCTs (ref numbers beginning METSECTVxxxxx)" https://download.schneider-electric.com/files?p_enDocType=Catalog&p_File_Name=PLSED309005EN_Web.pdf&... page 96. Same document also has page 103 with 0.333V 3-in-1 CTs with RJ45 for PM53x0R.
I do not believe the LVCTs mentioned in your post have the RJ45 connection at the end
Regards,
Charles.
Link copied. Please paste this link to share this article on your social media post.
Hello @swil ,
The catelog page for the PM5000 series has a note on the bottom "PM5310R and PM5320R must be used with Schneider Electric 3-in1 LVCTs (ref numbers beginning METSECTVxxxxx)" https://download.schneider-electric.com/files?p_enDocType=Catalog&p_File_Name=PLSED309005EN_Web.pdf&... page 96. Same document also has page 103 with 0.333V 3-in-1 CTs with RJ45 for PM53x0R.
I do not believe the LVCTs mentioned in your post have the RJ45 connection at the end
Regards,
Charles.
Link copied. Please paste this link to share this article on your social media post.
Thanks Charles. I didn't think that question through.
The LVCT meter won't be used in this case because the solid core LVCTs recommended in the PM5320R (LVCT meter) installation guide do not meet requirements.