Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION9000 Power Factor difference

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION9000 Power Factor difference
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
570
Mehran_Mehrnia
Mehran_Mehrnia Champion
202
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Related Products
product field
Schneider Electric
PowerLogic ION9000

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
mauricio_rojas_
mauricio_rojas_
Explorer

Posted: ‎2020-11-08 06:50 PM

0 Likes
2
2503
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-11-08 06:50 PM

ION9000 Power Factor difference

Hello everybody

 

Im looking for some guidance about an ION9000. The client has installed the meter in a LV system (3-Wire Grounded Wye) with a common current transformer with a sentronpac 3200. 

 

 
 

capture layout ion9k.PNG

 1. For power Factor, there are a big difference about the total factor (0.96 for ION9000 and 0.75 for sentronpac). We put a portatil meter (Fluke 435) and the Fluke reads also 0.75.  Is there any problem for the Total Power Factor in ION9000?  About the Current readings, the two meters have the same values.

 

2. About the ION9000 installation manual, we see that for 3-Wire Grounded Wye, there is only a MV graphic like below:

l.PNG

In order to correct the problem. How do we have to wire the meter  and its possible to fix the error in the total power factor reading?

 

 

Thanks in advance

 

  • Thumbnail of PowerLogic ION9000
    Schneider Electric
    PowerLogic ION9000
View products (1)
Labels
  • Labels:
  • ION9000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DanL
DanL Champion
Champion

Posted: ‎2020-11-09 10:16 AM

3 Likes
0
2493
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-11-09 10:16 AM

Issue 1: The LV system is described as a 3-wire grounded WYE. Let's assume that PTs are not used and the voltage wired to the meter is <690VLL. The best correct wiring and VOLTS mode to use would be the direct connect 4W-WYE where the meter's VN measuring terminal is connected to the common ground point of the power system.

Issue 2: The "Total Power Factor" on all ION meters is the ratio of the "Total kW" and the "Total kVA". Most likely they have the default configured "kVA Tot Method" = "Vector sum". The other device is likely implementing the equivalent of "Scalar Sum".

A large discrepancy is typical with non-linear loads or distorted signals.
IONReference\PowerMeterModule 

 

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 2
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-11-09 08:41 AM

0 Likes
1
2498
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-11-09 08:41 AM

Hello @mauricio_rojas_ ,

 

Looking at the data provided I am surprised to see the total PF so different from the individual phases. Where are you reading these numbers, software, web pages front panel? What are the readings for kw and kVA per phase and total? What is the kVA calculation method?

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
DanL
DanL Champion
Champion

Posted: ‎2020-11-09 10:16 AM

3 Likes
0
2494
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-11-09 10:16 AM

Issue 1: The LV system is described as a 3-wire grounded WYE. Let's assume that PTs are not used and the voltage wired to the meter is <690VLL. The best correct wiring and VOLTS mode to use would be the direct connect 4W-WYE where the meter's VN measuring terminal is connected to the common ground point of the power system.

Issue 2: The "Total Power Factor" on all ION meters is the ratio of the "Total kW" and the "Total kVA". Most likely they have the default configured "kVA Tot Method" = "Vector sum". The other device is likely implementing the equivalent of "Scalar Sum".

A large discrepancy is typical with non-linear loads or distorted signals.
IONReference\PowerMeterModule 

 

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.