PM5330 into JACE8000 over RTU

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM5330 into JACE8000 over RTU
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
478
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
89
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
DickyGray
DickyGray
Cadet

Posted: ‎2024-11-03 11:54 AM

0 Likes
3
395
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-03 11:54 AM

PM5330 into JACE8000 over RTU

Spoiler
Pm 5330 modbus rtu registers

Hi all,

I have some points that are being difficult to read. L3 to neutral just comes back as a null. L1 & L2 - N are fine. All of the Float Holding registers have required + 1 to read in Niagara. The L3-N hasn't liked with or without the +1. Also,  is the comms heartbeat available as a register ?

 

Any ideas ?

 

Thanks,

 

Richard

 

Labels
  • Labels:
  • PM5000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Jesus_Diaz
Lt. Commander Jesus_Diaz Lt. Commander
Lt. Commander

Posted: ‎2024-12-13 04:52 PM

0 Likes
0
290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-13 04:52 PM

Hi @DickyGray ,

 

 

If the data log was enabled in the PM5330, you may be able to extract the data from the meter using ION Setup.

 

You need to navigate to the data screen view (View > Data Screens) and enter Data Log #1. Here, you should be able to see the Active Energy Delivered and Received. Depending on the data log configuration, you may have different parameters in the log, but only two parameters can be enabled. Then, select the data you want to export (Ctrl + A to select all) and export it as a CSV file.

 

Best Regards,

JD

See Answer In Context

Reply
Replies 3
Jesus_Diaz
Lt. Commander Jesus_Diaz Lt. Commander
Lt. Commander

Posted: ‎2024-11-04 01:25 PM

1 Like
1
377
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-04 01:25 PM

Hi @DickyGray,

 

What is the power system configuration of the meter? Some power systems may not have L3-N values.

 

Could you also check the meter's front panel to see if the L3-N value is shown?

 

Additionally, please try using the Modbus Tester to read the registers.

 

Best regards,

JD

Reply
DickyGray
DickyGray
Cadet

Posted: ‎2024-12-11 02:19 AM

0 Likes
0
313
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-11 02:19 AM

Thanks JD,

We managed to get that working fine. 

 

We have another issue. Because the contractors didnt use the ION set tool for these, nothing has been done on the logs. What we want to do, but I am not sure if this can work, is :

Have a loss of comms alarm disable the logging at the Jace, on restoration of comms, retrieve the data not captured during comms loss.

i assume I need to get the logs sorted out on the meter via ION before this work. ?

 

Reply
Jesus_Diaz
Lt. Commander Jesus_Diaz Lt. Commander
Lt. Commander

Posted: ‎2024-12-13 04:52 PM

0 Likes
0
291
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-13 04:52 PM

Hi @DickyGray ,

 

 

If the data log was enabled in the PM5330, you may be able to extract the data from the meter using ION Setup.

 

You need to navigate to the data screen view (View > Data Screens) and enter Data Log #1. Here, you should be able to see the Active Energy Delivered and Received. Depending on the data log configuration, you may have different parameters in the log, but only two parameters can be enabled. Then, select the data you want to export (Ctrl + A to select all) and export it as a CSV file.

 

Best Regards,

JD

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of