Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Official documentation about Meters calibration ION 7550, ION 7650, ION 8000, PM 8000

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Official documentation about Meters calibration ION 7550, ION 7650, ION 8000, PM 8000
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
RogelioHdezD
RogelioHdezD Explorer
Explorer

Posted: ‎2023-10-03 04:30 PM

0 Likes
3
3148
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-10-03 04:30 PM

Official documentation about Meters calibration ION 7550, ION 7650, ION 8000, PM 8000

Hi,

Is there any SE official documents that describes if our meters require re-calibration and what is the procedure, requirements, periodicity, etc ? Customer requires this for energy audits.

Thanks

Rogelio Hdez

Technical Leader

GCP OPS

Labels
  • Labels:
  • ION7000
  • ION8000
  • PM8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2023-10-04 09:44 AM

1 Like
0
3126
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-10-04 09:44 AM

Hello @RogelioHdezD ,

 

For the ION7650/ION7550 there is a tech note 70072-0190-00. For ION8600 and ION8650 there is 70072-0193-01.  PM8000 is in the user guide - https://digital-energy-help.se.com/pm8000/en-us/content/18-accuracy/verifying-accuracy.htm?TocPath=V...

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Attachments
Reply
Replies 3
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2023-10-04 09:44 AM

1 Like
0
3126
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-10-04 09:44 AM

Hello @RogelioHdezD ,

 

For the ION7650/ION7550 there is a tech note 70072-0190-00. For ION8600 and ION8650 there is 70072-0193-01.  PM8000 is in the user guide - https://digital-energy-help.se.com/pm8000/en-us/content/18-accuracy/verifying-accuracy.htm?TocPath=V...

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Attachments
Reply
aniaqueen232
aniaqueen232
Explorer

Posted: ‎2023-10-04 11:04 AM

1 Like
0
3097
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-10-04 11:04 AM

For specific information on calibration requirements and procedures for Schneider Electric (SE) meters such as ION 7550, ION 7650, ION 8000, and PM 8000, it's best to refer to the official documentation provided by Schneider Electric. Here are steps you can take to access this information:

  1. Schneider Electric Website: Visit the Schneider Electric website (https://www.se.com) and navigate to the "Support" or "Documentation" section.

  2. Search for Your Meter Model: Use the search or product finder feature to locate the specific meter model you are interested in (e.g., ION 7550, ION 7650, ION 8000, PM 8000).

  3. User Manuals and Technical Documents: Look for user manuals, technical documentation, or application notes related to the meter model. These documents often contain information about calibration requirements, procedures, and periodicity.

  4. Contact Schneider Electric Support: If you cannot find the information you need on the website, consider reaching out to Schneider Electric's customer support or technical support team. They can provide guidance and direct you to the appropriate documentation.

  5. Consult Local Schneider Electric Representatives: In some cases, local Schneider Electric representatives or authorized service providers may be able to assist you with calibration requirements and procedures specific to your region or installation.

Reply
aniaqueen232
aniaqueen232
Explorer

Posted: ‎2023-10-04 11:05 AM

0 Likes
0
3072
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-10-04 11:05 AM

For specific information on calibration requirements and procedures for Schneider Electric (SE) meters such as ION 7550, ION 7650, ION 8000, and PM 8000, it's best to refer to the official documentation provided by Schneider Electric. Here are steps you can take to access this information:

  1. Schneider Electric Website: Visit the Schneider Electric website (https://www.se.com) and navigate to the "Support" or "Documentation" section.

  2. Search for Your Meter Model: Use the search or product finder feature to locate the specific meter model you are interested in (e.g., ION 7550, ION 7650, ION 8000, PM 8000).

  3. User Manuals and Technical Documents: Look for user manuals, technical documentation, or application notes related to the meter model. These documents often contain information about calibration requirements, procedures, and periodicity.

  4. Contact Schneider Electric Support: If you cannot find the information you need on the website, consider reaching out to Schneider Electric's customer support or technical support team. They can provide guidance and direct you to the appropriate documentation.

  5. Consult Local Schneider Electric Representatives: In some cases, local Schneider Electric representatives or authorized service providers may be able to assist you with calibration requirements and procedures specific to your region or installation.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore