Hi team,
My customer using PM5560 for tariff. Now, they just only logging Energy (kWh del). So, with memory 1.1Mb of PM5560.
I want know, when will Memory PM5560 full? 1 week, two week, or 1 month? Any document for calculator this logging in memory?
Thanks very much.
Link copied. Please paste this link to share this article on your social media post.
Hello @SESA528
The size of one data log record will be 20 bytes approximately for one energy parameter (INT64 data format). So the PM5560 can record the maximum of 60000 records when only 2 energy parameters are enabled (maximum 14 parameters can be enabled). This configuration can store the data records for about 21 months when the time interval selected for 15 minutes.
Please refer the attached excel sheet of data log calculator for more information.
Regards,
Ramasamy N
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hello @SESA528
The size of one data log record will be 20 bytes approximately for one energy parameter (INT64 data format). So the PM5560 can record the maximum of 60000 records when only 2 energy parameters are enabled (maximum 14 parameters can be enabled). This configuration can store the data records for about 21 months when the time interval selected for 15 minutes.
Please refer the attached excel sheet of data log calculator for more information.
Regards,
Ramasamy N