Hi Community,
Iv been asked by the customer on these questions, hoping to understand it better myself.
It is related power meters.
What is the Max segment size of the SBU Devices?
What is the SBU Window Settings?
What is the RTO Settings?
Many thanks
Link copied. Please paste this link to share this article on your social media post.
Hello @wasabi ,
I was able to find the following information:
MSS is the largest that will fit in the MTU which is 1500 bytes
Zero window is disabled, but the window can be smaller than the MSS
Minimum RTO is 1s, maximum is 60s.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @wasabi ,
I was able to find the following information:
MSS is the largest that will fit in the MTU which is 1500 bytes
Zero window is disabled, but the window can be smaller than the MSS
Minimum RTO is 1s, maximum is 60s.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
thank you sir, where can i find this information myself ?
Link copied. Please paste this link to share this article on your social media post.
Hello @wasabi ,
This is not information that you would have been able to find. I needed to reach out to developers for this information.
Regards,
Charles