Harmonic Compliance Report (IEEE519 report) no framework data detected

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Harmonic Compliance Report (IEEE519 report) no framework data detected
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All
Related Products
product field
PowerLogic
PowerLogic ION8650 series

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Liangchen1982
Ensign Liangchen1982
Ensign

Posted: ‎2024-12-09 10:59 AM

0 Likes
2
383
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-09 10:59 AM

Harmonic Compliance Report (IEEE519 report) no framework data detected

Hello SE expert,

 

I am using ION8650 and US ION template which comes with IEEE519 2014 template modules. All settings are configured properly, meters enabled in PME more than 7 days, however, when I run the Harmonic Compliance Report in web application, got error:  "No framework data detected. Check your device to ensure the correct framework is installed."

Liangchen1982_0-1733770704352.png

pls help guide how to fix this.

 

Thanks

Leo

  • Thumbnail of PowerLogic ION8650 series
    PowerLogic
    PowerLogic ION8650 series
View products (1)
Labels
  • Labels:
  • ION8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-12-10 09:08 AM

0 Likes
1
359
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-10 09:08 AM

Hello @Liangchen1982 ,

 

First suggestion I would have is confirm that the meter is indeed logging the measurements and that the measurement names match what PME is expecting. The measurement names as seen in PME would be like the following. Note that V1 would be duplicates to V2 and V3, I1 would be duplicated for I2 and I3.

519 Volt enum, 519 I_L, 519 I_SC, 519 Mx Dmd IL, V1-Hrm X, V1-Hrm X1, V1-Hrm X2, Valid XY, V-Hrm X1, V-Hrm X2, Invalid XY, V1-Hrm Z, V1-Hrm Z1, V1-Hrm Z2, Valid Z, V-Hrm Z1, V-Hrm Z2, Invalid Z, I1-Hrm X, I1-Hrm X1, I1-Hrm X2, I-Hrm X1, I-Hrm X2, I1-Hrm Y, I1-Hrm Y1, I1-Hrm Y2, I-Hrm Y1, I-Hrm Y2, I1-Hrm Z, I1-Hrm Z1, I1-Hrm Z2, I-Hrm Z1, I-Hrm Z2, V1 fund 10m, V1 H(x) % 10m, I1 fund 10m, I1 H(x) %D 10m, Voltage Total Harmonic Distortion 10-minute Mean on Input V1, Voltage Total Harmonic Distortion 10-minute Mean on Input V2, Voltage Total Harmonic Distortion 10-minute Mean on Input V3, I1 TDD 10m, I2 TDD 10m, I3 TDD 10m.

Note that PME measurement name and meter label may not always match. PME does sometimes have a mapping for example Voltage Total Harmonic Distortion 10-minute Mean on Input V3 is too long a label to fit on a meter.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 2
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-12-10 09:08 AM

0 Likes
1
360
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-10 09:08 AM

Hello @Liangchen1982 ,

 

First suggestion I would have is confirm that the meter is indeed logging the measurements and that the measurement names match what PME is expecting. The measurement names as seen in PME would be like the following. Note that V1 would be duplicates to V2 and V3, I1 would be duplicated for I2 and I3.

519 Volt enum, 519 I_L, 519 I_SC, 519 Mx Dmd IL, V1-Hrm X, V1-Hrm X1, V1-Hrm X2, Valid XY, V-Hrm X1, V-Hrm X2, Invalid XY, V1-Hrm Z, V1-Hrm Z1, V1-Hrm Z2, Valid Z, V-Hrm Z1, V-Hrm Z2, Invalid Z, I1-Hrm X, I1-Hrm X1, I1-Hrm X2, I-Hrm X1, I-Hrm X2, I1-Hrm Y, I1-Hrm Y1, I1-Hrm Y2, I-Hrm Y1, I-Hrm Y2, I1-Hrm Z, I1-Hrm Z1, I1-Hrm Z2, I-Hrm Z1, I-Hrm Z2, V1 fund 10m, V1 H(x) % 10m, I1 fund 10m, I1 H(x) %D 10m, Voltage Total Harmonic Distortion 10-minute Mean on Input V1, Voltage Total Harmonic Distortion 10-minute Mean on Input V2, Voltage Total Harmonic Distortion 10-minute Mean on Input V3, I1 TDD 10m, I2 TDD 10m, I3 TDD 10m.

Note that PME measurement name and meter label may not always match. PME does sometimes have a mapping for example Voltage Total Harmonic Distortion 10-minute Mean on Input V3 is too long a label to fit on a meter.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Liangchen1982
Ensign Liangchen1982
Ensign

Posted: ‎2024-12-10 11:30 AM

0 Likes
0
341
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-10 11:30 AM

we have figured out the issue: no more database room.

Thanks Charles.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of