Hello Yut,
Looking at the QuickION.cfg file in C:\Program Files (x86)\Schneider Electric\ION Setup\Tables\XXX\YYYY where XXX is the model and YYYY the display options, I see that the ION8800 meters do not include the MV-90 report option.
Likely you will need to log a case with Technical support (se.com-> support -> contact support) to have this tracked.
It may be possible to modify the .cfg file. A) Make a backup of the .cfg file and store in a safe location like desktop B) Edit the file with a text editor and replace the reports section with the text below.
Please note I do not have an ION8800 to test with right now.
Charles
[Reports]
TabCount=1
Tab1=Meter Info
Tab1Type=2
Tab1Text=Allows you to view/store meter information.
Tab1Buttons=1
Tab1Button1Label=Display
Tab1Button1=0,8
Tab1Registers=7
Tab1Reg1=10,1,0x0F80,Revenue Log
Tab1Reg1Text=This shows the meter revenue log information.
Tab1Reg2=10,1,0x0F89,EnergyDemand Log
Tab1Reg2Text=This shows the meter energydemand log information.
Tab1Reg3=10,1,0x1000,Event Log
Tab1Reg3Text=This shows the meter event information.
Tab1Reg4=10,1,0x3,Meter Configuration
Tab1Reg4Text=This reports the meter configuration information.
Tab1Reg5=10,1,0x4,Configuration Comparison
Tab1Reg5Text=This reports the differences between a stored meter configuration file and the present meter configuration.
Tab1Reg6=10,1,0x2,Template Comparison
Tab1Reg6Text=This reports the differences between a stored template and the meter template.
Tab1Reg7=10,1,0x5,MV-90 Report
Tab1Reg7Text=This reports information useful for MV-90 and allows saving info to a MV-90 Master file for importing.
Link copied. Please paste this link to share this article on your social media post.
Hello Yut,
Looking at the QuickION.cfg file in C:\Program Files (x86)\Schneider Electric\ION Setup\Tables\XXX\YYYY where XXX is the model and YYYY the display options, I see that the ION8800 meters do not include the MV-90 report option.
Likely you will need to log a case with Technical support (se.com-> support -> contact support) to have this tracked.
It may be possible to modify the .cfg file. A) Make a backup of the .cfg file and store in a safe location like desktop B) Edit the file with a text editor and replace the reports section with the text below.
Please note I do not have an ION8800 to test with right now.
Charles
[Reports]
TabCount=1
Tab1=Meter Info
Tab1Type=2
Tab1Text=Allows you to view/store meter information.
Tab1Buttons=1
Tab1Button1Label=Display
Tab1Button1=0,8
Tab1Registers=7
Tab1Reg1=10,1,0x0F80,Revenue Log
Tab1Reg1Text=This shows the meter revenue log information.
Tab1Reg2=10,1,0x0F89,EnergyDemand Log
Tab1Reg2Text=This shows the meter energydemand log information.
Tab1Reg3=10,1,0x1000,Event Log
Tab1Reg3Text=This shows the meter event information.
Tab1Reg4=10,1,0x3,Meter Configuration
Tab1Reg4Text=This reports the meter configuration information.
Tab1Reg5=10,1,0x4,Configuration Comparison
Tab1Reg5Text=This reports the differences between a stored meter configuration file and the present meter configuration.
Tab1Reg6=10,1,0x2,Template Comparison
Tab1Reg6Text=This reports the differences between a stored template and the meter template.
Tab1Reg7=10,1,0x5,MV-90 Report
Tab1Reg7Text=This reports information useful for MV-90 and allows saving info to a MV-90 Master file for importing.