MODBUS Import Module is missing in PM8000 ION Framework

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
Bojan
Captain Captain
Captain
0 Likes
4
388

MODBUS Import Module is missing in PM8000 ION Framework

I planned to use MODBUS Import Module to read Relay Word bits in SEL-751 Feeder Protection Relay from PM8000, but then I realized that the module is missing from the ION Framework.

What would be a replacement / work-around for it?

For example, how can I read the following MODBUS Slave SEL-751 logical 1 and 0 statuses from MODBUS Master PM8000 meter:


Accepted Solutions
Bojan
Captain Captain
Captain

Re: MODBUS Import Module is missing in PM8000 ION Framework

Patrick Lynch from Tech Support explained to me how to designate two bytes via the modbus master device module in ION Framework:

See Answer In Context

4 Replies 4
Yut
Captain
Captain

Re: MODBUS Import Module is missing in PM8000 ION Framework

Use Modbus Device Master module and Modbus Master Map module.

Bojan
Captain Captain
Captain
0 Likes
1
324

Re: MODBUS Import Module is missing in PM8000 ION Framework

Hi Yut,

I use Modbus Device Master module and Modbus Master Map module to read INT16 values, but how can I read the bit status from it?

In C# I would do the following, but have no idea how to program it in ION Framework:

Bojan
Captain Captain
Captain

Re: MODBUS Import Module is missing in PM8000 ION Framework

Patrick Lynch from Tech Support explained to me how to designate two bytes via the modbus master device module in ION Framework:

Yut
Captain
Captain
0 Likes
0
324

Re: MODBUS Import Module is missing in PM8000 ION Framework

I have an idea of Arithmetic Module compare the value to the mask value in decimal using IF function.