Alarm DAN6 Limit Exceeded 3 in PM8000

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

sesa101974_brid
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
4
359

Alarm DAN6 Limit Exceeded 3 in PM8000

Hi Experts,

PM8240 inform alarm in PME 8.1 software " DAN6 Limit Exceeded 3". So, What is the DAN6 Limit Exceeded 3. and Where I can setting value DAN6?

Thanks

DAN6.PNG

4 Replies 4
sesa101974_brid
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
2
293

Re: Alarm DAN6 Limit Exceeded 3 in PM8000

Help me!! Please

Robert_Lee
Captain Captain
Captain

Re: Alarm DAN6 Limit Exceeded 3 in PM8000

The DAN6 is referring to the "Disturbance Analyzer Module #6" which in the default framework is used for Current Swell alarm detection.

The default settings is for 155% over Current Nominal (which by default is set to 5 Amps) with a reset of 145%.

Go to the Alarm -> Sag/Swell and modify the I Swell Pickup limit or modify the Nominal current to the appropriate value.

The other number at the end probably refers to which of the 3 phases is exceeding the pickup limit (Phase A = 1, Phase B = 2, Phase C = 3) but you should check the ION Reference to be sure.

sesa101974_brid
Schneider Alumni (Retired)
Schneider Alumni (Retired)

Re: Alarm DAN6 Limit Exceeded 3 in PM8000

Hi Robert Lee,

Yes. Thanks for your information. Very helpful.

daniel_parker_p
Lieutenant
Lieutenant
0 Likes
0
293

Re: Alarm DAN6 Limit Exceeded 3 in PM8000

"DAN" I guess so that people don't have to refer to the DAM Limit?