Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION9000 digital output application

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Re: ION9000 digital output application
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
571
Mehran_Mehrnia
Mehran_Mehrnia Champion
203
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Szymon_Hochół
Szymon_Hochół Champion
Champion

Posted: ‎2020-09-10 03:16 AM

0 Likes
3
2276
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-09-10 03:16 AM

ION9000 digital output application

Hello Experts,

in one of our projects we are trying to replace A-Eberle's PQI-DA Smart power quality meter with our device. We want to use ION9000. PQI-DA has two digital outputs with fixed functionalities:

Przechwytywanie.JPG

 

Customer wants to collect these signals via controller in MV switchboard. So we need to program ION's outputs to perform in similar way. 

 

B01

The perfect solution would be to trigger digital output every time when ION's Diagnostic Module records a warning or failure event.

Przechwytywanie2.JPG

However, I couldn't figure out a way to find a register that we could use as a trigger in such approach. Any ideas?

 

B02

I'm thinking about merging pulses that trigger waveform recordings for sag/swell and transient. Additionaly, we could also use triggers from alarms in Setpoint Modules. Any of these would change the digital output state for 1s. What do you think about this? Maybe you have other ideas?

 

Any comment would be greatly appreciated here 🙂

 

Thank you, best regards

Labels
  • Labels:
  • ION Setup
  • ION9000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-09-12 01:28 PM

0 Likes
0
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-09-12 01:28 PM

Hello SHO,

 

I do not know of a single register that would be able to give you what you are looking for. The BIST register in the diagnostic module is close but this can have non-zero values that are not an issue for the device.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 3
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-09-11 10:37 AM

0 Likes
2
2266
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-09-11 10:37 AM

Hello @Szymon_Hochół ,

 

B01: I do not think there is a just a single register that could be used to determine the meter's state. The event register is used to write to the meter's onboard event log, it is not an ION register than can be linked to another module.

 

B02: Possible to link pulse merge module with different triggers to a oneshot timer module. Output from the Oneshot timer could then be used to drive the state of the output.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Szymon_Hochół
Szymon_Hochół Champion
Champion

Posted: ‎2020-09-11 11:47 AM

0 Likes
1
2263
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-09-11 11:47 AM

Hi @Charles_Murison

 

Thanks for your input 🙂 Do you have any suggestion on how to achieve anything possibly close to what B01 offers? Any mechanisms inside ION9000 to be notified about malfunctions?

 

Thanks

 

Have a good weekend 😉

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-09-12 01:28 PM

0 Likes
0
2260
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-09-12 01:28 PM

Hello SHO,

 

I do not know of a single register that would be able to give you what you are looking for. The BIST register in the diagnostic module is close but this can have non-zero values that are not an issue for the device.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore