Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

[ION9000][Summary] Technical FAQ

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • [ION9000][Summary] Technical FAQ
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2018-08-29 02:26 PM . Last Modified: ‎2019-04-05 02:22 PM

5 Likes
17
17274
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-08-29 02:26 PM

[ION9000][Summary] Technical FAQ

This ION9000 FAQ is intended to give an early release of technical information that relate to the release of the ION9000

 

Installation and Retrofit

 

Question:  Can the ION9000 fit into a ION7650 cutout.

Answer:     The ION9000 will fit into the existing cutout with no modifications.  The four studs fit into the corners and are secured with nuts.  Washers  will be placed between the panel and the adapter plate to limit the pressure on the gasket.

 

Question:  What is the current plan for the ION750 withdrawal?

Answer:     Most part numbers will be withdrawn after the ION9000 has been released for a year.  Exceptions include:  Low Voltage CT's, Low Voltage DC power supply, fiber ethernet, RMICAN, and OFGEM.

 

Display

 

Question:  Do I need to turn the meter off to swap / replace the display?

Answer:     Due to =S= safety policy, the meter must be powered down before working inside or on any power equipment.  The remote display can be hot swapped, as long as the user it not working inside a live cabinet.

 

Question:   Can the small PM8000 display be used on the ION9000.

Answer:     Yes however the small display must be upgraded to the minimum

 

Question:   Will the ION9000 display work on the PM8000.

Answer:     No.

 

Question:   Can you use two displays on the ION9000

Answer:     No the device only supports one display.

 

I/O

 

Question:  Do I need to turn the meter off to swap / replace the IO cards?

Answer:     Due to =S= safety policy, the meter must be powered down before working inside or on any power equipment.  Note that no damage will occur if it is done powered up; however, the cards will not be recognized until the next power up.

 

Question:  Can we use the ION9000 meters to trip the circuit breakers?

Answer:     Meter should not be used as protection device but it can be used as a control device for non-critical applications. Hence, we should not use it to trip the circuit breakers. but we can configure the meter to alarm on any PQ issue including harmonics.

 

Question:  What options are available for IO on the ION9000?

Answer:     Onboard:

                           - 8 Digital inputs with 24Vdc wetting voltage

                           - 4 Digital outputs (solid state)

                           - 2 form C relay outputs (rated for 8A @ 250V)

                  Expansion:

                           - Digital option module

                                o 6 Digital inputs with wetting voltage

                               o 2 form C relay outputs (rated for 8A @ 250V)

                          - Analog option module

                                o 4 Analog inputs (4 to 20mA or 0 to 30V)

                                o 2 Analog outputs (4 to 20mA or 0 to 10V)

 

Question:  How many options modules does the meter support?

Answer:    You may have up to 4 option cards attached to the meter at one time.

 

 

Logging:

 

Question:  What is the bandwidth of a captured waveform?

Answer:     The ION9000 introduces “extended waveform capture” that allows up to 30 cycles of pre-event waveform records at 1024 and 30 cycles of event data.  This waveform recorder can then be retriggered to extend the waveform for up to 180 cycles. It can then re-trigger that capture for a user defined number of captures limited by memory which is 2Gb for ION9000.

 

Question:  Is the ION9000 memory expandable?

Answer:    The ION9000 has 2 GB of memory by default.   A future enhancement will allow the installation of a micro SD memory card that can be up to 32 GB.

 

Question:  What is the max length of a waveform recorder?

Answer:     ION9000 has 2GB onboard memory, the ION7650 has 10MB. ION9000 can store up to 10MB per channel for waveforms (this could be minutes for each channel.

 

 

Web Pages

 

Question:  Will digital certificates be available for HTTPs?

Answer:     A default certificate will be shipped from manufacturing, however it is recommended customers create their own certificate and load it onto the meter.

 

Communications

 

Question:  Can the meter communicate with two Modbus Masters?

Answer:     Yes

 

Question:  What communcations hardware does the device support?

Answer:     The ION9000 supports 2 Ethernet ports and 2 RS485 ports.

 

Question:  Can the Ethernet communications ports be daisy chained?

Answer:     Yes

 

Specifications

 

Question:  Could you please elaborate on the savings calculation for extra accuracy?

Answer: The calculations can be in the whitepaper: A high accuracy standard for electricity meters​

Question:  Will the external CT's influence the meters accuracy claims?

Answer:    It is in the benefit of the customer to have accurate CT's however by not doing so will not change the fact the meter is twice as precise than any competitors meter.

 

Question:  What is the new standard for class 0.1S accuracy? When will it be published?

Answer:     Accuracy requirements for IEC class 0.1S will be in the 2nd edition of IEC62052-11/IEC62053-22; publiction is expected in 2018; this standard will not allow "partial" compliance with class requirements;Accuracy requirements for ANSI class 0.1 are in the ANSI C12.20-2015 (NEMA 2017).

 

Question:  What's the difference between class 0.1 and 0.1S?

Answer:     Technically, only class 0.1S will be part of the IEC62053-22 standard. The "S" refers to the meter accuracy and range characteristics which should match the characteristics of an external "S" class transformer to ensure optimal performance.

 

Question:  Why do the current connections need to be so robust if the max current that will flow there is 5A?

Answer:     The specification for the ION9000 is for the current inputs to be rated to 20A continuous, so they have been designed to handle this amount of current.  The “robust” look is mainly due to the requirement to have “captured” screws, which is partly driving the size and spacing of each input.  The other factor driving the spacing is the size of the active current transformers

 

Question:  What is the accuracy for harmonic readings?

Answer:     2.0% per IEC 61557-12 for both voltage & current.

 

Question:  Can the ION9000 detect a low battery?

Answer:     There are event log entries when the meter real-time clock battery gets low. It is also available as a diagnostic register via ION and could be exposed via other protocols (ex Modbus) by customizing the meter configuration.

 

TimeSyncing

 

Question:  What timesync options are available on the ION9000?

Answer:      • Time synchronization is possible via:

                         Precision network time protocol (PTP) based on IEEE 1588 / IEC 61588.

                         GPS clock (RS-485) or IRIG-B (digital input) to ±1 millisecond.

                         Network Time Protocol (NTP/SNTP).

                         Automatic time synchronization available through Schneider Electric software server.

 

Event Notification

 

Question:  What event notification options are available?

Answer:     Meter has alarming and control function:

                         - 50+ definable alarms to log critical event data, trigger waveform recording,

or perform control function.

                         - Trigger on any condition, with 1/2-cycle and 1-second response time.

                         - Combine alarms using Boolean logic enabling customization of alarms.

                         - Alarm notification via email.

                         - In conjunction with Schneider Electric’s EcoStruxure software, alarms,software alarms, and alarm frequency are categorized and trended

enabling sequence of events and root cause analyses.

 

 

Features

Question:  Will supra-harmonics be supported?

Answer:     The initial release will not support supra-harmonics, however it is currently on the radar for a future release.

 

Question:  Is there a cyber security standard ION9000 will comply with?

Answer:     We will be standardizing on IEC62443, however compliance will not come with the first release.  We will complete PEN testing and be working towards Achilies certification.

 

Question:  Will the ION9000 be RMICAN certified?

Answer:     Yes, however the RMICAN process can only be started after production units are manufactured, certification typically can take up to a year to accomplish.

 

Question:  What are the current plans for OFGEM and CoP options?

Answer:     Once production units are available  we will be seeking approvals for Cop 1, 2 and 3, during this process the existing ION7650 OFGEM references will remain active.

 

Question:  Will the Low Voltage CT option be available?

Answer:     This will not be available at launch, currently it is proposed for the R2 release in 2020.

 

Question:  What improvements are we making to ION modules?

Answer:     On 1st release module types are very similar to the selection available on the ION7650; however, some module types will see a 30% increase in capacity.

 

Question:  Will the ION9000 support IEEE519?

Answer:     Yes, The evaluation applied in the ION9000 will be according to the 2014 version of the standard.

 

 

Question:  Will ION9000 R1 include PQDIF?

Answer:     PQDIF support is provided through PME software.  The meter natively provides COMTRADE files for all captured waveforms.

 

Question:  How do you configure the device to capture waveforms of short circuit current before and after it trips a breaker?

Answer:    The meter can capture a waveform on short circuit current and breaker trip in a couple of ways.   First on short circuit current, you could configure a current swell alarm with a setpoint high enough to prevent nuisance alarms yet within the range of the measurement CT to prevent clipping.  If you wanted to be very sure, you could use a Boolean to combine a current swell with a voltage dip.  This would give you a short circuit indication.  For breaker trip, the easiest way is to connect the trip contact from the breaker into an input on the meter and trigger a waveform from that input.  The meter can capture several cycles prior to the event, so small delays are no issue.

 

Question:  What types of disturbances is Disturbance Direction Detected triggered on?

Answer:     Disturbance Direction Detection (DDD) is applied for “disturbance alarms” which include sags (dips), swells and transients (ION7650)

 

Question:  Why have 5 measureable currents on the device?

Answer:     5 current inputs can be used to measure 3 phase + Neutral + Ground currents. The ground current can offer an indication of Power Quality issues in the system

 

Question:

Answer:

 


This document was generated from the following discussion: ION9000 - Technical FAQ

 

 

Labels
  • Labels:
  • PM Guidebooks
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-02-26 04:35 PM

0 Likes
0
16807
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-26 04:35 PM

If anybody else is looking for this answer, this has been answered in a different thread.

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 17
richard_schwass
richard_schwass
Explorer

Posted: ‎2018-09-24 10:21 PM

0 Likes
0
17228
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-09-24 10:21 PM

What is the processing power increase (from the ION7650) available to ION customisation?

Reply
Yut
Yut
Leader

Posted: ‎2018-09-24 11:16 PM

0 Likes
1
17226
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-09-24 11:16 PM

NICT(current probe) version when will it be available ?

Reply
Daniel_Brandao
Daniel_Brandao Mentor
Mentor

Posted: ‎2018-10-05 09:33 AM

0 Likes
0
17199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-10-05 09:33 AM

The plan, subject to change, is to have NICTs available in this offer mid 2020.

Reply
JamesAZZO
JamesAZZO
Leader

Posted: ‎2018-11-25 10:24 PM

0 Likes
1
17135
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-11-25 10:24 PM

Where can we find the default Modbus Map for the ION9000? Manual just say search the Schneider Website.

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2018-12-12 12:00 PM

0 Likes
0
17116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-12-12 12:00 PM

https://www.schneider-electric.ca/en/faqs/FA362601/

L4 Prime for Advanced metering and Utilities
Reply
Anonymous user
Not applicable

Posted: ‎2019-02-26 08:51 PM

0 Likes
0
17063
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-02-26 08:51 PM

do you have offline simulator ION9000 ? please share to my email: rizqy.sultan@se.com

Reply
ShaunTaylor
ShaunTaylor Contributor
Contributor

Posted: ‎2019-02-27 05:22 AM

0 Likes
7
17059
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-02-27 05:22 AM

Re Memory

 

We have ION7650's being replaced with ION9000's. On moving the Designer frameworks across, the ION9000 runs out of memory. Is there a workaround or fix available? I would have expected more modules and more memory to be available in the 9000.

 

Regards,

Shaun

Reply
Tom_Stevenson
Tom_Stevenson Champion
Champion

Posted: ‎2019-02-27 08:36 AM . Last Modified: ‎2019-02-27 12:43 PM

0 Likes
3
17055
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-02-27 08:36 AM

Hi Shaun - good to hear from you.  Hoping you can elaborate on "out of memory" a bit.  I have attached an image of what I assume you are seeing.  There are many more modules available on the ION9000 vs. the 7650, so right now I am assuming that you are seeing module obsolescence vs. being out of memory.  If this is the case, the first thing to note is that there are new harmonics modules (same as PM8000/7400) that replace the ones the 7650 had - this is in order to support new standards and updated standards.  To make an ION9000 framework, I would suggest you save any custom logic as sub-frameworks from your 7650 and then paste those on a default ION9000 framework.

 

Let us know

 

Thanks


Tom

 

 

 

 

Attachments
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2019-02-27 05:34 PM

1 Like
2
17042
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-02-27 05:34 PM

Hello Shaun

 

In Desinger, there are 2 different ways to paste a framework. Locked paste and non locked paste. Do you know which version you were doing? The locked paste will overwrite the module numbers, the unlocked paste will add the next available module. Therefore if a full ION7650 framework is pastes on the ION9000, it would be almost equivelent to 2 separat frameowrks being pasted on the meter. Almost is important as many modules are only present once in a meter's template, therefore the paste will fail as the module already exists.

 

There are a number of features, standards etc that depend on specific components being present in the meter. A lock paste could potentiall overwrite some of this without overwriting the entire section of framework. Therefore I do not recommend pasting the entire ION7650 framework onto the ION9000 meter. As Tom mentioned, it is possible to paste a framelet that has just the custom work.

 

Charles

L4 Prime for Advanced metering and Utilities
Reply
ShaunTaylor
ShaunTaylor Contributor
Contributor

Posted: ‎2019-02-28 03:55 AM

0 Likes
2
17039
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-02-28 03:55 AM

Hi Tom, yes you too - time for another trip to the UK?

 

This issue happended with a couple of engineers in our team so I will see if they have some screenshots or detail to add here. 

@sesa208600_brid (Zoltan) and @Andy_Hubert please could you elaborate on the issues. I believe the error message was memory related however.

 

Regards

Shaun

Reply
ShaunTaylor
ShaunTaylor Contributor
Contributor

Posted: ‎2019-02-28 04:03 AM

0 Likes
1
17038
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-02-28 04:03 AM

Hi Charles,

 

Thanks for your response and suggestions. The engineers who have had these issues are very experienced and understand the lock paste vs non lock so this is not likely to be the issue. They were simply loading a custom framework same as they have previously done in ION7650's, but this time in an ION9000. 

 

Kind regards

Shaun

Reply
ShaunTaylor
ShaunTaylor Contributor
Contributor

Posted: ‎2019-02-28 07:27 AM

0 Likes
1
17036
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-02-28 07:27 AM

Hi Tom

 

...update, @sesa208600_brid Zoltan updated the firmware on the ION9000 to the latest and now he is able to paste the modules. I believe he could not paste more than 59 data recorder modules before this. Seems ok now 🙂

Reply
Tom_Stevenson
Tom_Stevenson Champion
Champion

Posted: ‎2019-02-28 08:19 AM

0 Likes
0
17033
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-02-28 08:19 AM

Hi Shaun - did you have a beta unit by chance?  We have an imminent maintenance release coming, but only the released firmware exists for the ION9000 right now, so I am a bit confused by the "upgraded firmware" resolution.

 

We are also interested in any insights the team had in porting their 7650 frameworks to the 9K so we can collect best practices.

 

I hope to make it to the UK again !  I am not in a marketing role at this point, so I am not travelling as much these days.

 

Thanks !

 

Tom

Reply
sesa208600_brid
sesa208600_brid Explorer
Explorer

Posted: ‎2019-03-14 04:44 AM

0 Likes
0
17011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-03-14 04:44 AM

Hi guys,

 

the problem with pasting the framework was sorted out after the meter was upgraded to v2. 

 

regards,

zoltan

Reply
sesa54412_bridg
sesa54412_bridg Contributor
Contributor

Posted: ‎2019-05-03 02:57 PM

3 Likes
2
16953
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-05-03 02:57 PM

Note of clarification on the harmonic accuracy for the ION9000:

 

The ION9000 has better than 1% accuracy according to IEC 61557-12 for both voltage and current.


The ION9000 has full and traceable compliance to IEC 62586-1 as a PQI-A-FI1.
A component of this compliance includes IEC 61000-4-30 Class A performance.
The harmonic accuracy required for Class A performance varies from 0.05% to 0.8% of nominal.

 

A NMi BV Certin issued PQI-A-FI1 certificate for the ION9000 can be shared by request to the Offer Manger:

Daniel Brandao:  @Daniel_Brandao 

 

A whitepaper providing an overview of Power Quality Instruments (PQI) can be found here: Link

Reply
sesa108084_brid
sesa108084_brid Explorer
Explorer

Posted: ‎2020-02-25 06:58 PM

0 Likes
1
16814
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-25 06:58 PM

Good day 

 

Is ion9000 equipped with c37.118 sychronophasor function?

 

TQ

 

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2020-02-26 04:35 PM

0 Likes
0
16807
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-26 04:35 PM

If anybody else is looking for this answer, this has been answered in a different thread.

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore