PM8000 Digital Output at startup

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8000 Digital Output at startup
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
MaxRose
Lieutenant | EcoXpert Master MaxRose Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-02-19 04:12 AM

1 Like
13
4458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-19 04:12 AM

PM8000 Digital Output at startup

Hello,

 

PM8000 Digital IOs expansion module, we realize that when meter does a powerup and at this point some output should be at one , all outputs relays are at OFF, even if the Digital output module (in Designer) is at ON (because of some condition). I found in ION reference guide for Digital Output that when a meter do a powerup , all force outputs are at OFF. The only way to make them goes OK is when some output condition change. Does the meter wait for a transition Rising Edge after a powercyle? Is there any way to make them be at the starting good status? Any idea?  Thanks

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
MaxRose
Lieutenant | EcoXpert Master MaxRose Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-02-20 01:11 PM

0 Likes
6
4421
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-20 01:11 PM

Here you go!

See Answer In Context

Attachments
Reply
Replies 13
Omaelk
Janeway Omaelk
Janeway

Posted: ‎2020-02-19 05:03 AM

0 Likes
0
4453
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-19 05:03 AM

Hey @MaxRose , thank you for your question
 
I moved it to the Power Metering forum where the community of experts will be able to provide you the right support and solve your issue! 
 
PS: don't hesitate to check the Knowledge base and/or use the search bar with keywords. there is a lot of content discussed everyday and your issue may have already been solved 😉

 

 

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2020-02-19 01:32 PM

1 Like
11
4452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-19 01:32 PM

Hello @MaxRose ,

 

This is a very loaded question as there could be many different modules that can change the digital output state (but only 1 at any given time). For example the calibration pulse module could be linked to Port 1.So even if Digital output module is 1, the state of port is not changed until Calibration module changes the state.

 

Note that during power-up the outputs of the meter are non-deterministic. Only after the meter has finished initializing can we know for sure what the state ill be.

 

Charles

L4 Prime for Advanced metering and Utilities
Reply
MaxRose
Lieutenant | EcoXpert Master MaxRose Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-02-19 01:44 PM

1 Like
10
4451
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-19 01:44 PM

Thanks,

 

Finally I use pulse from Diagnostic module (the one that pulse after a power up) when meter power up to start a 10 sec timer.

In from of each Digital Outputs, I used  Setpoint (greater than 0) as an interface to get a Enable/Disable module (that Digital Output do not have), so all my logic are in front of the setpoints. When 10 seconds timer started , I Disable Setpoints module wich force every Outputs to 0 (OFF).

When Timer is done, I enable Setpoints and it does see transition from logic to 1.

 

I found that below 5 seconds it is risky to miss that pulse to the timer. So better longer o be safe.

 

Thanks

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2020-02-19 01:53 PM

1 Like
9
4447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-19 01:53 PM

Hello,

 

Do you have a template you would be willing to share with me? I'd like to test this some time. No promises I'll be able to find anything.

 

Charles

L4 Prime for Advanced metering and Utilities
Reply
MaxRose
Lieutenant | EcoXpert Master MaxRose Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-02-20 11:04 AM . Last Modified: ‎2020-02-20 11:36 AM

0 Likes
8
4440
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-20 11:04 AM

Yes,

 

Here is framework, just add your logic in front of Setpoints.

 

I just don't know how to share or send framework on community. I can't attach it to message.

Attachments
Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2020-02-20 12:39 PM

0 Likes
7
4424
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-20 12:39 PM

Please also attache the configuration of the module named "Port A D1".
Both the input link configuration and the setup registers.

Reply
MaxRose
Lieutenant | EcoXpert Master MaxRose Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-02-20 01:11 PM

0 Likes
6
4422
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-20 01:11 PM

Here you go!

Attachments
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2020-02-21 08:36 PM

0 Likes
5
4414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-21 08:36 PM

Hello,

 

Are you able to start a tech support case? I would like to track this with a case to make sure this gets looked at.

 

Thank you,

Charles

L4 Prime for Advanced metering and Utilities
Reply
MaxRose
Lieutenant | EcoXpert Master MaxRose Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-02-24 07:26 AM

0 Likes
4
4410
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-24 07:26 AM

Hello ,

 

Yes

 

Case reference #: 67614655 

 

Thanks

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2020-02-25 03:32 PM

0 Likes
3
4402
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-25 03:32 PM

Hello, 

 

What type and how many IO modules do you have on this device?

 

I'll need this info to try and reproduce in house.

 

Charles

L4 Prime for Advanced metering and Utilities
Reply
MaxRose
Lieutenant | EcoXpert Master MaxRose Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-02-26 05:48 AM

0 Likes
2
4399
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-26 05:48 AM

Hello,

 

IOs on meter itself (3In/1Out wich I don't really use in my project) + 2x Discret IO Cards METSEPM89M2600 (2 x (6in/2out))

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2020-02-26 03:53 PM

0 Likes
1
4394
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-26 03:53 PM

Hello MaxRose,

 

When I tested this on a meter at my desk, I setup a framelet to have a set point module, triggered from an external numeric, write to relay output of expansion IO module. When I powered up my meter I started a timer, after ~35 seconds, I heard the relay "click". Depending on the framework as well as firmware, this time could also change.

 

When you tested with your meter how long did you wait?

L4 Prime for Advanced metering and Utilities
Reply
MaxRose
Lieutenant | EcoXpert Master MaxRose Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-02-26 04:25 PM

0 Likes
0
4392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-26 04:25 PM

10 sec was ok.

 

I installed latest pm8000 firmware

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of