Help
  • Explore Community Expore Community
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Explore Community Explore Community
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • EcoStruxure Asset Advisor
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

PM8000 Digital Output at startup

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8000 Digital Output at startup
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
307
Ramasamy_N
Captain Ramasamy_N Captain
78
DanL
Captain DanL Captain
72
Robert_Lee
Captain Robert_Lee Captain
68
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
MaxRose
Ensign MaxRose
Ensign

Posted: ‎2020-02-19 04:12 AM

1 Like
13
3341
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-19 04:12 AM

PM8000 Digital Output at startup

Hello,

 

PM8000 Digital IOs expansion module, we realize that when meter does a powerup and at this point some output should be at one , all outputs relays are at OFF, even if the Digital output module (in Designer) is at ON (because of some condition). I found in ION reference guide for Digital Output that when a meter do a powerup , all force outputs are at OFF. The only way to make them goes OK is when some output condition change. Does the meter wait for a transition Rising Edge after a powercyle? Is there any way to make them be at the starting good status? Any idea?  Thanks

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
MaxRose
Ensign MaxRose
Ensign

Posted: ‎2020-02-20 01:11 PM

0 Likes
6
3304
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-20 01:11 PM

Here you go!

See Answer In Context

Attachments
Reply
Replies 13
Omaelk
Administrator Omaelk Administrator
Administrator

Posted: ‎2020-02-19 05:03 AM

0 Likes
0
3336
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-19 05:03 AM

Hey @MaxRose , thank you for your question
 
I moved it to the Power Metering forum where the community of experts will be able to provide you the right support and solve your issue! 
 
PS: don't hesitate to check the Knowledge base and/or use the search bar with keywords. there is a lot of content discussed everyday and your issue may have already been solved 😉

 

 

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2020-02-19 01:32 PM

1 Like
11
3335
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-19 01:32 PM

Hello @MaxRose ,

 

This is a very loaded question as there could be many different modules that can change the digital output state (but only 1 at any given time). For example the calibration pulse module could be linked to Port 1.So even if Digital output module is 1, the state of port is not changed until Calibration module changes the state.

 

Note that during power-up the outputs of the meter are non-deterministic. Only after the meter has finished initializing can we know for sure what the state ill be.

 

Charles

L4 Prime for Advanced metering and Utilities
Reply
MaxRose
Ensign MaxRose
Ensign

Posted: ‎2020-02-19 01:44 PM

1 Like
10
3334
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-19 01:44 PM

Thanks,

 

Finally I use pulse from Diagnostic module (the one that pulse after a power up) when meter power up to start a 10 sec timer.

In from of each Digital Outputs, I used  Setpoint (greater than 0) as an interface to get a Enable/Disable module (that Digital Output do not have), so all my logic are in front of the setpoints. When 10 seconds timer started , I Disable Setpoints module wich force every Outputs to 0 (OFF).

When Timer is done, I enable Setpoints and it does see transition from logic to 1.

 

I found that below 5 seconds it is risky to miss that pulse to the timer. So better longer o be safe.

 

Thanks

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2020-02-19 01:53 PM

1 Like
9
3330
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-19 01:53 PM

Hello,

 

Do you have a template you would be willing to share with me? I'd like to test this some time. No promises I'll be able to find anything.

 

Charles

L4 Prime for Advanced metering and Utilities
Reply
MaxRose
Ensign MaxRose
Ensign

Posted: ‎2020-02-20 11:04 AM . Last Modified: ‎2020-02-20 11:36 AM

0 Likes
8
3323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-20 11:04 AM

Yes,

 

Here is framework, just add your logic in front of Setpoints.

 

I just don't know how to share or send framework on community. I can't attach it to message.

Attachments
Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2020-02-20 12:39 PM

0 Likes
7
3307
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-20 12:39 PM

Please also attache the configuration of the module named "Port A D1".
Both the input link configuration and the setup registers.

Reply
MaxRose
Ensign MaxRose
Ensign

Posted: ‎2020-02-20 01:11 PM

0 Likes
6
3305
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-20 01:11 PM

Here you go!

Attachments
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2020-02-21 08:36 PM

0 Likes
5
3297
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-21 08:36 PM

Hello,

 

Are you able to start a tech support case? I would like to track this with a case to make sure this gets looked at.

 

Thank you,

Charles

L4 Prime for Advanced metering and Utilities
Reply
MaxRose
Ensign MaxRose
Ensign

Posted: ‎2020-02-24 07:26 AM

0 Likes
4
3293
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-24 07:26 AM

Hello ,

 

Yes

 

Case reference #: 67614655 

 

Thanks

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2020-02-25 03:32 PM

0 Likes
3
3285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-25 03:32 PM

Hello, 

 

What type and how many IO modules do you have on this device?

 

I'll need this info to try and reproduce in house.

 

Charles

L4 Prime for Advanced metering and Utilities
Reply
MaxRose
Ensign MaxRose
Ensign

Posted: ‎2020-02-26 05:48 AM

0 Likes
2
3282
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-26 05:48 AM

Hello,

 

IOs on meter itself (3In/1Out wich I don't really use in my project) + 2x Discret IO Cards METSEPM89M2600 (2 x (6in/2out))

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2020-02-26 03:53 PM

0 Likes
1
3277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-26 03:53 PM

Hello MaxRose,

 

When I tested this on a meter at my desk, I setup a framelet to have a set point module, triggered from an external numeric, write to relay output of expansion IO module. When I powered up my meter I started a timer, after ~35 seconds, I heard the relay "click". Depending on the framework as well as firmware, this time could also change.

 

When you tested with your meter how long did you wait?

L4 Prime for Advanced metering and Utilities
Reply
MaxRose
Ensign MaxRose
Ensign

Posted: ‎2020-02-26 04:25 PM

0 Likes
0
3275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-26 04:25 PM

10 sec was ok.

 

I installed latest pm8000 firmware

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc