Dear Experts,
I have a request form a big customer, is there any datasheet of technical document where I can find the temperature coefficient in (% / °C) I have found that the datasheet refers to compliance with IEC 62053-22 standard, but the client needs it to be specified in a schneider document in order to compare with others brands.
picture provided by customer
Picture provided by customer from a Landis meter
I'll look forward for your answer
Best regards,
Juan Quintanilla
Link copied. Please paste this link to share this article on your social media post.
The ION8650 is designed and tested to comply to IEC accuracy Class 0,1S for In = 1A and Imax = 20A
For compliance to IEC 62053-22, eight meters were tested at Kema Labs under various conditions:
- seven load levels ranging between 0.05A and 20A, at both unity PF and 50% Lag
- six different temperatures spanning -25 deg C and +55 deg C
The maximum temperature coefficient measured for energy accuracy was 0.002% / K (only one meter registered this "high" and only between 45 degC and 55degC). All other test points for all meters were <= 0.001% / K
Most tests had no measurable drift.
The typical/average temperature coefficient for ION8650 is < 0.001% / K (ie. <10 ppm/C)
The acceptable limits specified in the standard for Class 0,1S are:
at cos(phi) = 1, from 0.01A to 20A: 0.005%/K
at cos(phi) = 0.5, from 0.05A to 20A: 0.010%/K
Link copied. Please paste this link to share this article on your social media post.
The ION8650 is designed and tested to comply to IEC accuracy Class 0,1S for In = 1A and Imax = 20A
For compliance to IEC 62053-22, eight meters were tested at Kema Labs under various conditions:
- seven load levels ranging between 0.05A and 20A, at both unity PF and 50% Lag
- six different temperatures spanning -25 deg C and +55 deg C
The maximum temperature coefficient measured for energy accuracy was 0.002% / K (only one meter registered this "high" and only between 45 degC and 55degC). All other test points for all meters were <= 0.001% / K
Most tests had no measurable drift.
The typical/average temperature coefficient for ION8650 is < 0.001% / K (ie. <10 ppm/C)
The acceptable limits specified in the standard for Class 0,1S are:
at cos(phi) = 1, from 0.01A to 20A: 0.005%/K
at cos(phi) = 0.5, from 0.05A to 20A: 0.010%/K