Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION8650 - Change SMTP Port

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION8650 - Change SMTP Port
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Related Products
product field
PowerLogic
PowerLogic ION8650 series

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
CamboHeath
CamboHeath
Troubleshooter

Posted: ‎2025-06-23 07:38 PM

0 Likes
4
2308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-06-23 07:38 PM

ION8650 - Change SMTP Port

Hi there, 

 

I am trying to change the default SMTP port of an ION8650 from the default (161) to a new port to enable emails via a customers SMTP server. I can not find how to achieve this in either ION Reference or the ION8650 manual.

 

CamboHeath_0-1750732270410.png

 

SMTP is not a protocol that can have its port changed in the "Protocols" menu in IONsetup.

 

CamboHeath_3-1750732419380.png

CamboHeath_4-1750732433019.png

 

Attempting to add a custom port to the end of the SMTP server address per ION Reference does not allow for the change to save as the address can only be saved in the format aaa.bbb.ccc.ddd.

 

CamboHeath_5-1750732559582.png

 

Can anyone advise how to change the SMTP port in an ION8650 meter?

 

 

  • Thumbnail of PowerLogic ION8650 series
    PowerLogic
    PowerLogic ION8650 series
View products (1)
Labels
  • Labels:
  • ION Setup
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2025-06-24 09:33 PM

1 Like
0
2247
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-06-24 09:33 PM

Hi @CamboHeath 

 

As the documentation team has already been notified, the typo will be corrected.

 

Since an optional port is not allowed for the ION8650, regardless of whether the IP is static or not, a possible workaround is to set up a mail relay that listens on port 25 (which is compatible with the ION8650) and forwards mail to your actual SMTP server on the desired port.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

See Answer In Context

Reply
Replies 4
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2025-06-24 12:50 AM . Last Modified: ‎2025-06-24 12:51 AM

0 Likes
0
2290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-06-24 12:50 AM

Hi @CamboHeath 

 

The default SMTP (Simple Mail Transfer Protocol) server port number is 25. Port 161, is used by SNMP (Simple Network Management Protocol), which is used for network management and monitoring. I'm not sure why port 161 is mentioned for the SMTP server in the ION8650 user guide.

 

As mentioned per each Module's description in ION Reference:

Mehran_Mehrnia_1-1750750627753.png

 

The ION8650 is primarily designed for utility-grade metering and may have limited flexibility where configurations are standardized. Therefore optional port is not allowed for ION8650:

Mehran_Mehrnia_2-1750750983879.png

 

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2025-06-24 10:33 AM

0 Likes
1
2263
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-06-24 10:33 AM

Please note that the document version shown is 03, the latest version is 06 (https://www.se.com/ca/en/download/document/7EN02-0306/) If you use online guide you can see that the Port and name have been corrected (https://product-help.schneider-electric.com/PowerLogic-ION8650/en-us/content/06-communications/ether...)

 

After talking with developer I confirmed that ION8650 Meter with V4.40.1 firmware does not accept domain names for SMTP server. I have sent a comment to the team that maintains the user guide documents.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
CamboHeath
CamboHeath
Troubleshooter

Posted: ‎2025-06-24 06:28 PM

0 Likes
0
2255
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-06-24 06:28 PM

Hi Charles,

 

Both links you sent through show the default SMTP port as 161. Noting that this is not correct and it should be 25 based on Mehran's comment.

 

Independent of domain name, if i have a Static IP for a SMTP server is there any way to change the default SMTP port? If not then the ION8650 will not be fit for purpose for this application.

 

Thankyou.

 

CamboHeath_0-1750814233736.png

CamboHeath_1-1750814269726.png

 

Reply
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2025-06-24 09:33 PM

1 Like
0
2247
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-06-24 09:33 PM

Hi @CamboHeath 

 

As the documentation team has already been notified, the typo will be corrected.

 

Since an optional port is not allowed for the ION8650, regardless of whether the IP is static or not, a possible workaround is to set up a mail relay that listens on port 25 (which is compatible with the ION8650) and forwards mail to your actual SMTP server on the desired port.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore