Ask our Experts
Didn't find what you are looking for? Ask our experts!
Dear Community Members, We are currently experiencing a technical issue that is affecting the ability to create new posts. Our team is actively investigating the root cause and working to resolve it as quickly as possible. We apologize for the inconvenience and appreciate your patience. SE Community Team!
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Link copied. Please paste this link to share this article on your social media post.
Hi Xperts,
Can the iEM 3000 series kilowatt-hour meters provide "Neutral Current" readings? We have checked the modbus registry address and it seems it is not there.
Furthermore, is there a workaround for this?
These meters are to be daisy chained to a PAS800L.
Thanks in advance,
Jiedan
Link copied. Please paste this link to share this article on your social media post.
Hello @jedzruiz1985
iEM3000 series meters does not support the "Neutral Current" readings at present.
Regards,
Ramasamy N
Link copied. Please paste this link to share this article on your social media post.
Hello @jedzruiz1985
iEM3000 series meters does not support the "Neutral Current" readings at present.
Regards,
Ramasamy N
Link copied. Please paste this link to share this article on your social media post.
Hi Ramasamy,
Thanks for your reply. Is there a workaround on this? like creating a custom model on EPC-W?
Regards,
Jiedan
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.