Hi Xperts,
Can the iEM 3000 series kilowatt-hour meters provide "Neutral Current" readings? We have checked the modbus registry address and it seems it is not there.
Furthermore, is there a workaround for this?
These meters are to be daisy chained to a PAS800L.
Thanks in advance,
Jiedan
Link copied. Please paste this link to share this article on your social media post.
Hello @jedzruiz1985
iEM3000 series meters does not support the "Neutral Current" readings at present.
Regards,
Ramasamy N
Link copied. Please paste this link to share this article on your social media post.
Hello @jedzruiz1985
iEM3000 series meters does not support the "Neutral Current" readings at present.
Regards,
Ramasamy N
Link copied. Please paste this link to share this article on your social media post.
Hi Ramasamy,
Thanks for your reply. Is there a workaround on this? like creating a custom model on EPC-W?
Regards,
Jiedan