ION8650 /8800 IEC 61850 report control block

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
Yut
Captain
Captain
0 Likes
11
3613

ION8650 /8800 IEC 61850 report control block

We try to connect the ION meter to SCADA/HMI (ION8800/ION8650) using IEC 61850.

The SCADA use the CID file from meter as reference urcbMMXU01 to urcbMMXU04 but the meter send them with 01 at end. We try to configure the OptFields seqNum to false but when the CID file was upload back to meter we got Invalid CID file.

 

CID file

<ReportControl bufTime="1000" buffered="false" confRev="1" datSet="MMXU" desc="Unbuffered Measurements Report" indexed="false" intgPd="0" name="urcbMMXU01" rptID="urcbMMXU1">
<Private type="SchneiderElectric-SFT-IsPredefined"/>
<TrgOps dchg="true" dupd="false" period="true" qchg="true"/>
<OptFields configRef="true" dataRef="false" dataSet="true" reasonCode="true" seqNum="true" timeStamp="true"/>
</ReportControl>

 

 

Screen shot from scanner the 01 was added monitor from Wireshark also show that the meter add 01. Please advice how the 01 would be eliminated.

 

IEC6185urbc1.png

Tags (1)

Accepted Solutions
Charles_Murison
Picard Picard
Picard
8
3600

Re: ION8650 /8800 IEC 61850 report control block

Hello Yut,

 

I did a bit of investigation and can confirm that the 01 at the end of the name is due to feature described by the IEC 61850 standard, called indexing*. This can be a little misleading as the meter only supports a single subscription to each report but supports 4 "copies" of the report, each with a different name.

 

* IEC 61850-7-2 Edition 2, Communication networks and systems for power utility automation – Part 7-2: Basic information and
communication structure – Abstract communication service interface(ACSI), 2010.

https://cms-cdn.selinc.com/assets/Literature/Publications/Technical%20Papers/6912_LessonsLearned_BW_... page 4 for more information if desired.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
11 Replies 11
Sanjeet_Sahota
Lieutenant Lieutenant
Lieutenant
0 Likes
1
3605

Re: ION8650 /8800 IEC 61850 report control block

Hi Yut,

 

Can you share which firmware version you are using?


Regards,

Sanjeet

Tags (1)
Charles_Murison
Picard Picard
Picard
8
3601

Re: ION8650 /8800 IEC 61850 report control block

Hello Yut,

 

I did a bit of investigation and can confirm that the 01 at the end of the name is due to feature described by the IEC 61850 standard, called indexing*. This can be a little misleading as the meter only supports a single subscription to each report but supports 4 "copies" of the report, each with a different name.

 

* IEC 61850-7-2 Edition 2, Communication networks and systems for power utility automation – Part 7-2: Basic information and
communication structure – Abstract communication service interface(ACSI), 2010.

https://cms-cdn.selinc.com/assets/Literature/Publications/Technical%20Papers/6912_LessonsLearned_BW_... page 4 for more information if desired.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
Yut
Captain
Captain
0 Likes
0
3592

Re: ION8650 /8800 IEC 61850 report control block

for the ION8800 V370

ION8650 004.031.001

Tags (1)
Yut
Captain
Captain
0 Likes
0
3591

Re: ION8650 /8800 IEC 61850 report control block

The index option in the CET850 was unchecked.

 

We will do further experiment on both side.

Tags (1)
Yut
Captain
Captain
0 Likes
6
3588

Re: ION8650 /8800 IEC 61850 report control block

OK I got it. The RptEna is False. So I have to study CET850 how to set it to True.

RptEna.png

Tags (1)
Charles_Murison
Picard Picard
Picard
0 Likes
5
3585

Re: ION8650 /8800 IEC 61850 report control block

RptEna  is true when IEC 61850 client has successfully subscribed to the report on the meter. It is not a variable that can be "set" from outside the meter.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
Yut
Captain
Captain
0 Likes
4
3580

Re: ION8650 /8800 IEC 61850 report control block

Any suggestion to let the customer be able to get report with their SCADA/HMI ?

Tags (1)
Charles_Murison
Picard Picard
Picard
0 Likes
3
3578

Re: ION8650 /8800 IEC 61850 report control block

Have the SCADA/HMI use indexing as defined in the standard?!?

 

I am guessing the name difference is why the client is not getting data from the meter.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
Yut
Captain
Captain
0 Likes
2
3394

UntRe: ION8650 /8800 IEC 61850 report control block

Until now no solution for this issue . The customer's SCADA/HMI has no option for handle an extra 01 pad to the name the software read from whatever is in CID file only.

 

Does anyone on earth has solution ? 

Tags (1)
Yut
Captain
Captain

Re: UntRe: ION8650 /8800 IEC 61850 report control block

Latest  update

Customer can read now in HMI set whatever indicate in CET850 Sevices>Report settings.

Done.

 
 

 

Tags (1)
Yut
Captain
Captain
0
3289

Re: UntRe: ION8650 /8800 IEC 61850 report control block

Using IEC61850 with  NR HMI/SCADA