ION7650 - Configuring Watchdog and Event present digital outputs

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION7650 - Configuring Watchdog and Event present digital outputs
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
sesa207714_brid
sesa207714_brid Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2016-02-11 02:26 AM

0 Likes
1
841
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-02-11 02:26 AM

ION7650 - Configuring Watchdog and Event present digital outputs

Hi,

Has anyone configured the digital outputs on the ION7650 for either a watchdog, or an Alarm/Event being present on the system?

Currently the customer has asked for the ION meters to be configured with a Watchdog/health contact. This will stay closed until the meter loses power, then it should reopen. I'm assuming it would be easily achieved using the solid state digital outputs, but I have no way off testing it as the customer does not want to power the meter down.

In regard to the event present output, I wave looked and noticed that there are a lot of statuses for when waveforms have been captured that can be ORed together in the VIP frameworks for the meter, but there does not seem to be any single status for when the meter has captured an alarm/event or waveform. Is this correct, or have i missed this signal somewhere?

Thanks for all of your assistance.

Regards,

Martin

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Yut
Captain Yut
Captain

Posted: ‎2016-02-14 07:59 PM

0 Likes
0
789
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-02-14 07:59 PM

To indicate that the meter is ON please take a look at the Diagnostics module there is one output called Power Up Pulse you can use it to trigger the Force On input of the Digital Output assigned to one of the three output mechanical relays the  set up for digital out put Polarity must be Inverted when power up the state of the relay will change when power down the relay will drop.

For the Sag/Swell and Transient module there some status and trigger output which you can use as alarm. But do not use the meter as relay especially when some customer ask for DNP signal called Unsolicited Response in ION meter this function always disabled.

See Answer In Context

Reply
Reply 1
Yut
Captain Yut
Captain

Posted: ‎2016-02-14 07:59 PM

0 Likes
0
790
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-02-14 07:59 PM

To indicate that the meter is ON please take a look at the Diagnostics module there is one output called Power Up Pulse you can use it to trigger the Force On input of the Digital Output assigned to one of the three output mechanical relays the  set up for digital out put Polarity must be Inverted when power up the state of the relay will change when power down the relay will drop.

For the Sag/Swell and Transient module there some status and trigger output which you can use as alarm. But do not use the meter as relay especially when some customer ask for DNP signal called Unsolicited Response in ION meter this function always disabled.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of