Hi,
I would like the latest firmware files for the ION7330 meter.
Link copied. Please paste this link to share this article on your social media post.
Hello @darkenwald
Note that ION7300 series of meters have 2 different hardware versions. You can tell the hardware version based on the serial numer's last 2 digits.
If the last two digits are <= 09, it is a Revision A meter (example PA-0005A123-06)
If the last two digits are >= 10, it is a Revision B meter (example PA-0005A123-11)
Revision B firmware cannot be applied to Revision A hardware and revision A firmware cannot be applied to Revision B hardware. Please confirm what hardware version you need.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @darkenwald
Note that ION7300 series of meters have 2 different hardware versions. You can tell the hardware version based on the serial numer's last 2 digits.
If the last two digits are <= 09, it is a Revision A meter (example PA-0005A123-06)
If the last two digits are >= 10, it is a Revision B meter (example PA-0005A123-11)
Revision B firmware cannot be applied to Revision A hardware and revision A firmware cannot be applied to Revision B hardware. Please confirm what hardware version you need.
Regards,
Charles