Hi All,
Wondering if this alarm is triggered when voltage is lost? (like the outage of power system)
Also wondering interruption seems to be a serious issue, but why the default priority is Low?
Thanks
Link copied. Please paste this link to share this article on your social media post.
Hello @Stuart_Cheng ,
Voltage interruption is based on the 4-30 definition:
The alarm comes from the Disturbance Analyzer Module (DAN)
The alarm level is something that can be customized. If customer wants this to be high, the priority can be changed.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @Stuart_Cheng ,
Voltage interruption is based on the 4-30 definition:
The alarm comes from the Disturbance Analyzer Module (DAN)
The alarm level is something that can be customized. If customer wants this to be high, the priority can be changed.
Regards,
Charles