Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Link copied. Please paste this link to share this article on your social media post.
Hi All,
Wondering if this alarm is triggered when voltage is lost? (like the outage of power system)
Also wondering interruption seems to be a serious issue, but why the default priority is Low?
Thanks
Link copied. Please paste this link to share this article on your social media post.
Hello @Stuart_Cheng ,
Voltage interruption is based on the 4-30 definition:
The alarm comes from the Disturbance Analyzer Module (DAN)
The alarm level is something that can be customized. If customer wants this to be high, the priority can be changed.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @Stuart_Cheng ,
Voltage interruption is based on the 4-30 definition:
The alarm comes from the Disturbance Analyzer Module (DAN)
The alarm level is something that can be customized. If customer wants this to be high, the priority can be changed.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.