How do I configure the PM2200/PM5000 when the customer is using PT (Potential Transformer) with a voltage rating of 600V/400V, which is higher than the default selection of (>120V)?
Link copied. Please paste this link to share this article on your social media post.
Hello @Samart_Ploypradab ,
You can keep the ratio the same x/120 = 600/400, x = 180.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @Samart_Ploypradab ,
You can keep the ratio the same x/120 = 600/400, x = 180.
Regards,
Charles