ION 8650 network TCP/IP Stack

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION 8650 network TCP/IP Stack
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Andy_Taylor
Lieutenant | EcoXpert Master Andy_Taylor Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2019-09-12 05:28 PM

0 Likes
7
1983
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-09-12 05:28 PM

ION 8650 network TCP/IP Stack

My company (APT) supports a local customer with a large installed base of ION 8600 and ION 8650 meters.

 

This customer is updating their network infrastructure, which involves migrating from an existing Cisco-based switch infrastructure to a new ESDN (Enterprise Software Defined Networking) network infrastructure.  Unfortunately, we are having significant issues getting the ION 8600/8650 meters to work with the new infrastructure. The underlying issue is that the ION 8600/8650 meters do not appear to generate any outbound network traffic when initially connected to the network, and thus the ESDN network cannot map the device into its connected device table. 

 

We really need to get connected with someone at Schneider Electric who really understands the TCP/IP stack in the ION 8600/8650 meters so they can help our ESDN engineering team debug and resolve the issue. The meters themselves do not seem to have any configuration or diagnostic features that we can find to resolve this problem.

 

We can certainly try tech support for this issue, but we understand this is NOT a typical tech support response item.  Appreciate any help, and especially further discussion on networking requirements for devices.

 

Regards,

Andy

Tags (1)
  • Tags:
  • 8650
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Andy_Taylor
Lieutenant | EcoXpert Master Andy_Taylor Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2019-09-18 04:42 PM

0 Likes
1
1976
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-09-18 04:42 PM

@Hal_Etheridge 

Hal:

 

Appreciate your suggestion - but that won't work as a solution for this customer.

 

This client is looking for large scale solution to implement at the meter level so that any of these meters are deployed the meter is configured to generate an ARP request when connected to the network.

 

        Possible work arounds being considered - NTP time synch, MeterMail, and even DNS on those meters that support it.

 

The point of ESDN is to NOT require connecting to every device from another computer, so the work arounds above might be the solution.

 

Do you have any other suggestions for work arounds that we could configure on the meter itself?

 

Regards,

Andy

See Answer In Context

Reply
Replies 7
Hal_Etheridge
Janeway Hal_Etheridge Janeway
Janeway

Posted: ‎2019-09-12 08:25 PM

0 Likes
2
1981
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-09-12 08:25 PM

Power cycling the device should force it to generate an ARP request.  Likewise on every IP address change an ARP request should be triggered to confirm the new IP is not being used.  Otherwise the device will not be generating any traffic because it is a *server* and not a client.

 

The IP address is typically static for servers (those without DNS support anyway) so can you not just connect the device to the network and try and communicate to it from another computer?  That should just generate an ARP broadcast request from the computer to the network segment that the destination IP address is supposed to be on.  Once received that will trigger the device to send an ARP response and thus register itself with the networking infrastructure.

Reply
Andy_Taylor
Lieutenant | EcoXpert Master Andy_Taylor Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2019-09-18 04:42 PM

0 Likes
1
1977
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-09-18 04:42 PM

@Hal_Etheridge 

Hal:

 

Appreciate your suggestion - but that won't work as a solution for this customer.

 

This client is looking for large scale solution to implement at the meter level so that any of these meters are deployed the meter is configured to generate an ARP request when connected to the network.

 

        Possible work arounds being considered - NTP time synch, MeterMail, and even DNS on those meters that support it.

 

The point of ESDN is to NOT require connecting to every device from another computer, so the work arounds above might be the solution.

 

Do you have any other suggestions for work arounds that we could configure on the meter itself?

 

Regards,

Andy

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2019-09-23 03:59 PM

0 Likes
0
1966
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-09-23 03:59 PM

Hello Andy,

 

Another possibility along the lines of what you are already thinking is setting a meter up as a Modbus master via Ethernet connection. This would also force a meter to initiate an outbound connection when connected to the network. The IP address of the device does not even need to exist.

L4 Prime for Advanced metering and Utilities
Reply
Liangchen1982
Ensign Liangchen1982
Ensign

Posted: ‎2023-11-03 09:24 AM

0 Likes
1
1291
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-03 09:24 AM

Hello,

Do we have a fix for this issue? I met another similar issue with CAISO ION8650 meters in US needs to be addressed.

Thanks

Leo

 

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2023-11-06 09:20 AM

0 Likes
0
1288
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-06 09:20 AM

Hello @Liangchen1982 ,

The answer is the same, the ION8650 meters will not make an outbound connection unless programmed to do so. The easiest why to program a meter to make an outbound connection is to make meter modbus master something that does not exist. When the read now input of the Modbus device Module is pulsed, the meter would try to connect, this would force meter that send message out on the network.

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Liangchen1982
Ensign Liangchen1982
Ensign

Posted: ‎2023-11-10 10:58 AM

0 Likes
1
1252
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-10 10:58 AM

Thanks @Charles_Murison , I am planning to test it in our lab with a testing ION8650 meter. Is there an easy way to replicate the issue so I could test the framework?

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2023-11-14 09:44 AM

0 Likes
0
1249
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-14 09:44 AM

Hello @Liangchen1982 ,

 

Each network is going to be unique so there is no formal test for this.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of