ION Setup can't connect to PM8000

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
Szymon_Hochół
Commander Commander
Commander
0 Likes
2
540

ION Setup can't connect to PM8000

Hi all,

I have a problem trying to connect to PM8240 using ION Setup. After typing meter's IP adress in browser, the web server works fine, however ION Setup shows an error. I'm using v3.0.18075.02 of the software. Please see the screenshot attached. 

 

Any ideas?

 

BR

Untitled.jpg

Tags (2)

Accepted Solutions
Jose_Moreno
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
1
539

Re: ION Setup can't connect to PM8000

Is ION over TCP enabled?

On the webpage: Setup -> Ethernet -> Advanced settings

See Answer In Context

2 Replies 2
Jose_Moreno
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
1
540

Re: ION Setup can't connect to PM8000

Is ION over TCP enabled?

On the webpage: Setup -> Ethernet -> Advanced settings

Szymon_Hochół
Commander Commander
Commander

Re: ION Setup can't connect to PM8000

It was disabled, turning it back on solved the issue.

 

Thanks a lot!

 

BR