Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Posted: 2023-04-11 06:58 PM . Last Modified: 2024-01-30 04:34 AM
Link copied. Please paste this link to share this article on your social media post.
i have an EGX300 (Power Link G3) that must be integrate by Modbus TCP/IP, This in turn has a BCPM in the Network. Currently i have alrready managed to add the device to the EBO Modbus network, however i cannot find any modbus register map that helps me indicate the Corresponging Modbus registers.
Link copied. Please paste this link to share this article on your social media post.
Maybe this is what you need https://www.se.com/ww/en/download/document/BCPM_Modbus_and_BACnet-REV_D/
Link copied. Please paste this link to share this article on your social media post.
Maybe this is what you need https://www.se.com/ww/en/download/document/BCPM_Modbus_and_BACnet-REV_D/
Link copied. Please paste this link to share this article on your social media post.
Thank you, it was very helpful.