i have an EGX300 (Power Link G3) that must be integrate by Modbus TCP/IP, This in turn has a BCPM in the Network. Currently i have alrready managed to add the device to the EBO Modbus network, however i cannot find any modbus register map that helps me indicate the Corresponging Modbus registers.
Link copied. Please paste this link to share this article on your social media post.
Maybe this is what you need https://www.se.com/ww/en/download/document/BCPM_Modbus_and_BACnet-REV_D/
Link copied. Please paste this link to share this article on your social media post.
Maybe this is what you need https://www.se.com/ww/en/download/document/BCPM_Modbus_and_BACnet-REV_D/
Link copied. Please paste this link to share this article on your social media post.
Thank you, it was very helpful.