ION Setup - Modem port numbers

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
poneill_premium
Lieutenant | EcoXpert Master Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master
0 Likes
4
446

ION Setup - Modem port numbers


ION Setup will only let you choose port number 1 to 16 when connecting using a modem.

Any way this can be extended?

Client has a couple of digiboxes and modems configured up to com port 40.

Paula O'Neill

Accepted Solutions
Robert_Lee
Captain Captain
Captain
0 Likes
0
424

Re: ION Setup - Modem port numbers

Typically C:\ProgramData is a hidden folder not typically visible using Windows Explorer.

But in case you are storing the file elsewhere, use the following steps to confirm:

1.  Click on the checkbox icon on the ION Setup toolbar (or select Tools -> Options from the menus).

2. This should display the following dialog.  Highlight the bottom edit box and select <Ctrl> + C to copy to the clipboard.

3. Open Windows Explorer and paste into the address bar at the top.  You should be able to find the IONSETUP.INI file there (or at least some files of some sort).  If not, then the installer likely could not install the requisite files and you will likely need to reinstall using the Administrator account.

See Answer In Context

4 Replies 4
Robert_Lee
Captain Captain
Captain

Re: ION Setup - Modem port numbers

This is controlled using the IONSETUP.INI.

Using Notepad (or any other text editor), go to the C:\ProgramData\Schneider Electric\ION Setup folder and open the IONSETUP.INI file.

Near the top of the file you'll find the section heading [Communications] and you'll see the following lines:

[Communications]

SerialPorts=16

Edit the number to a higher value and restart ION Setup.

Note that there is a maximum # of sites that ION Setup presently supports (this has been growing during the evolution of ION Setup and presently is over 4000) and increasing the number dedicated to serial port use reduces the number available for Ethernet use (both direct and those used for gateways) but unless you have an extremely large number, this shouldn't be an issue.

poneill_premium
Lieutenant | EcoXpert Master Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master
0 Likes
1
424

Re: ION Setup - Modem port numbers

Hi Robert,

We have checked on a couple of versions of ION Setup but there is no IONSETUP.INI file.

(Including 3.0 Build number 3.018214.03).

Is it particular to a particular version?

Thanks,

Paula

Paula O'Neill
Robert_Lee
Captain Captain
Captain
0 Likes
0
425

Re: ION Setup - Modem port numbers

Typically C:\ProgramData is a hidden folder not typically visible using Windows Explorer.

But in case you are storing the file elsewhere, use the following steps to confirm:

1.  Click on the checkbox icon on the ION Setup toolbar (or select Tools -> Options from the menus).

2. This should display the following dialog.  Highlight the bottom edit box and select <Ctrl> + C to copy to the clipboard.

3. Open Windows Explorer and paste into the address bar at the top.  You should be able to find the IONSETUP.INI file there (or at least some files of some sort).  If not, then the installer likely could not install the requisite files and you will likely need to reinstall using the Administrator account.

poneill_premium
Lieutenant | EcoXpert Master Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master
0 Likes
0
424

Re: ION Setup - Modem port numbers

Got it. Thanks Robert.

Paula O'Neill