Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION Meter - PSO ION Driver with L Modifier appended to ION Output

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION Meter - PSO ION Driver with L Modifier appended to ION Output
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Gavin_Bryson
Gavin_Bryson
Mentor

Posted: ‎2023-04-26 08:15 PM

0 Likes
6
2696
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-04-26 08:15 PM

ION Meter - PSO ION Driver with L Modifier appended to ION Output

Hi,

 

I know this has PSO in its topic but it relates to how PSO reads data for Active Energy and Reactive Energy. The driver uses the following Output labels from the ION Meter to read Active and Reactive Energy. The pipe symbol is used as alternative labels may be used for different ION meters. (See below) 

 

Active Energy

kWh del-rec|kWh net|Real Energy|Real Energy Signed;L

 

Reactive Energy

kVARh del-rec|kVARh net|Reactive Energy|Reactive Energy Signed|kQh net;L

 

The question I have relates to the ';L' modifier and what it relates to.  I've included a screenshot of the ION Driver help from PSO for info.

Gavin_Bryson_0-1682564828213.png

 

By using ';L' data is read from data log(s).

 

So, I'm doing some testing on a customer site and there isn't currently a load however there are Energy readings displayed in the Meter from some of the limited testing we did with a load and what was present from the Schneider factory.

 

When attempting to read Active and Reactive Energy via PSO I don't see a value. Equally when I use ION Setup to view the Data Log, the log is empty.

 

Does anyone know what may be preventing the Data Log from updating so that I can read the Energy values? I've reviewed the meter settings using ION Setup ad logging has been enabled.

 

Any advice would be greatly appreciated.

 

Kind regards,

 

Gavin

 

Labels
  • Labels:
  • ION Setup
  • ION9000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2023-05-03 09:19 AM

0 Likes
0
2627
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-03 09:19 AM

Hello @Gavin_Bryson ,

If no recorders this would suggest meter does not have a template. If some recorders and there but not the recorders you are expecting then customized template has not been uploaded.

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 6
N4th4n13L
N4th4n13L Troubleshooter
Troubleshooter

Posted: ‎2023-04-27 07:07 AM

0 Likes
0
2684
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-04-27 07:07 AM

Hello @Gavin_Bryson,

 

I had a couple of questions when reading the log with ION Setup. Do you specify a data range or just do a read all? If the time wasn't set correctly when the data logging occurred it might get missed by pulling a specific date range, but will still show up if you do a read all.

 

Also, was any change made to the data recorders after testing? Whether changing the sources or depth? Any change to the data recorder will wipe it...

 

Lastly, was the meter in test mode when testing was done? Test mode typically disables most of the integrators so the accumulation from testing doesn't get applied to the meters revenue framework.

Reply
Tom_Stevenson
Tom_Stevenson Champion
Champion

Posted: ‎2023-04-27 10:05 AM

0 Likes
1
2681
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-04-27 10:05 AM

Likely more information required, but just confirming "EgyDmd Log Enbl" is set to true.  Those parameters are logged by the "EgyDmd Log" and are set to log out of the factory.  Custom framework?

Reply
Tom_Stevenson
Tom_Stevenson Champion
Champion

Posted: ‎2023-04-27 10:10 AM

0 Likes
0
2681
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-04-27 10:10 AM

If it is not a custom framework, and it is factory framework V4.0.0.0.0, also confirm "Ignre Dmd if TS" is set to false/0

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2023-04-27 04:41 PM

0 Likes
2
2673
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-04-27 04:41 PM

Hello @Gavin_Bryson ,

 

There are a lot of different elements to check that would not do well over this forum. Strongly recommend working with your local technical support to investigate this. One test you can do with ION Setup is place in Advanced configuration mode. Navigate to Data recorders then recorder in question. Hold shift and clink on the input tab, this should show you real time values. Confirm the enable is true and the record input is non zero.

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Gavin_Bryson
Gavin_Bryson
Mentor

Posted: ‎2023-05-03 09:17 AM

0 Likes
1
2628
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-03 09:17 AM

Ok, thanks @Charles_Murison

I did view the recorders using the method you outlined and there was nothing there.

 

I will check the information posted here and if I identify an issue I will contact technical support.

 

Many thanks,

 

Gavin

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2023-05-03 09:19 AM

0 Likes
0
2627
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-03 09:19 AM

Hello @Gavin_Bryson ,

If no recorders this would suggest meter does not have a template. If some recorders and there but not the recorders you are expecting then customized template has not been uploaded.

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore