ION9000 onboard I/O bad quality IEC 61850

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION9000 onboard I/O bad quality IEC 61850
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
neracali
Ensign neracali
Ensign

Posted: ‎2023-04-26 05:07 AM

0 Likes
7
2026
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-04-26 05:07 AM

ION9000 onboard I/O bad quality IEC 61850

Hi All,

 

Our client needs to give monitoring of measurements and breaker status & control to the utility company from ION9000 via 61850 protocol.

We followed instructions and download .cid file to the ION9000.

All measurements and statuses are correct except statuses contained in GGIO dataset (onboard IO).
These indications always have bad quality(invalid timestamp 1.1.1970.) with values 0.
On several inputs we have HI state that is correct interpreted on web interface.

The same situation is when these inputs are mapped as custom Inputs (dataset CUSTOMIO).

Device firmware is 003.000.000, feature set standard.

As I can see the same .icd file is in several firmware releases.

 

Any change in the .cid file didn't run correctly (eg. change or add datasets or change RCB).

RTU is ABB RTU560, but the same symptom occurs with IEC Browser (screenshots attached).

Any idea how to solve this? 

Could someone check onboard IO statuses in own ION9000 with eg. IEC browser?

 

 

Attachments
Labels
  • Labels:
  • ION9000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
neracali
Ensign neracali
Ensign

Posted: ‎2023-05-04 12:36 AM

0 Likes
0
1907
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-04 12:36 AM

Hi @Charles_Murison and all,

After ION FW upgrade to 4.0.0 everything works well with the same .cid file.
Timestamp for all inputs with state "1" is current timestamp, and "0" for lowered inputs.
Thank you very much.

neracali_0-1683123307625.png

 

See Answer In Context

Reply
Replies 7
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2023-04-26 10:44 AM

0 Likes
1
2020
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-04-26 10:44 AM

Hello @neracali ,

 

Likely you will want to contact technical support to start troubleshooting this. One place you can start looking is with ION Setup software -> Advanced configuration -> IEC61850GGIO onb Modules -> IEC61850GGIO onb 1. If you hold shift and click on input tab you might see real time values linked to this module.

Digital output may not be able to read ONB1_GGIO1.SPCSO1.stVal if controlled by IEC61850. Have not tested linking to custom Digital IO.

 

I used IED Explorer and was able to read Input status (all false since nothing connected to inputs.) 

Charles_Murison_0-1682531044572.png

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
neracali
Ensign neracali
Ensign

Posted: ‎2023-04-28 01:31 AM

0 Likes
0
2010
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-04-28 01:31 AM

Hi @Charles_Murison,

 

Thanks for your effort.

There is the same problem with your device.

Please check timestamps of the signals on your screenshot. They are not updated.
What Firmware version is your device?

Onboard inputs are well interpreted in web and ION Setup in my case.

 

Attachments
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2023-04-28 03:09 PM

0 Likes
3
2000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-04-28 03:09 PM

Hello @neracali ,

 

I do not have a meter currently where the digital inputs are connected and have changed state. Without this state change, the timestamp will be "0" as you have already seen in screenshots. The device I was connected to has V3.1.0 firmware.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
neracali
Ensign neracali
Ensign

Posted: ‎2023-04-30 07:05 AM

0 Likes
2
1990
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-04-30 07:05 AM

Hi @Charles_Murison ,

 

according the IEC 61850 & IEC 60870-5 General interrogation should return current input state with current timestamp (trigger options GI & period are true in ION9000 .cid file).
There is no sense to show input value only on data change, since ION restart or RTU/SCADA restart will generate fake and bad quality values.
It looks like 61850 server doesn't gather Onboard IO input values. 

neracali_0-1682863240431.png

 

 

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2023-05-01 09:12 AM

0 Likes
1
1960
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-01 09:12 AM

Hello @neracali ,

 

"General interrogation should return current input state with current timestamp" Technically the IEC61850 module does this. On the meter itself, the timestamp for the register will be reset if meter loses power and input is not active when meter powers back up. Below is a test I did with Input 1 on ION9000T meter. You can see that IEC61850 does report the state of the Digital input correctly.

I used ION Setup to connect to the meter in advanced configuration. Hold shift with clicking the output registers to get the current real time value. In the output registers you can hold <Ctrl> down and click on S1 state to send specific messages to the meter to read time of the register. IEC61850 module in the meter does essentially the same thing.

Below are the steps I performed:
1) Meter powered on, digital inputs never connected.

Charles_Murison_0-1682957058468.pngCharles_Murison_1-1682957070442.png

 


2) Connected input to 24V to trigger a state change

Charles_Murison_2-1682957091876.pngCharles_Murison_3-1682957102268.png

 


3) Input disconnected

Charles_Murison_4-1682957119782.pngCharles_Murison_5-1682957130014.png



4) Meter Power cycled, while input is disconnected.

Charles_Murison_6-1682957161384.pngCharles_Murison_7-1682957171053.png

 


5) Meter power cycled while input connected

Charles_Murison_8-1682957185078.pngCharles_Murison_9-1682957195805.png

 

Regards,

Charles

 

 

 

L4 Prime for Advanced metering and Utilities
Reply
neracali
Ensign neracali
Ensign

Posted: ‎2023-05-03 06:34 AM

0 Likes
0
1925
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-03 06:34 AM

Thank You @Charles_Murison.

In this case (ION900T) quality in all cases is well ([NONE]), despite of strange timestamp values ("0" after restart).
In your first post quality of physical input information was bad, as in my case ([VALIDITY1] - Bad Timestamp), and that is the main problem. Also, in my case Input values are incorrect only on 61850 interface.

I'll try to upgrade Firmware of the device to the latest (as soon as I get permission), and check if anything is going to change.

Reply
neracali
Ensign neracali
Ensign

Posted: ‎2023-05-04 12:36 AM

0 Likes
0
1908
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-04 12:36 AM

Hi @Charles_Murison and all,

After ION FW upgrade to 4.0.0 everything works well with the same .cid file.
Timestamp for all inputs with state "1" is current timestamp, and "0" for lowered inputs.
Thank you very much.

neracali_0-1683123307625.png

 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of