Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION 7650 energy calculation

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION 7650 energy calculation
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
571
Mehran_Mehrnia
Mehran_Mehrnia Champion
203
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
joel_mora_soati
joel_mora_soati
Contributor

Posted: ‎2021-04-29 12:03 PM

0 Likes
3
3248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-04-29 12:03 PM

ION 7650 energy calculation

Hello experts,

 

I have a customer asking about how ION Meter do energy calculations. He made a manual calculation to compare energy calculated manually to meter calculation as image attached.

 

Just the "error" and "Intervalo de energía activa CALCULADA" columns are calculated, the other ones are using ION meter variables outputs took from PME.

 

The formula used by customer for manual energy was:

 

((SUM of three phase currents* AVG Three Phase Voltage * ^3 * Power Factor)/4000) It is also a image attached "formula"

 

The customer now is asking me why is a big difference between calculations and measured value. I wonder if you can help me to justificate technically that ION meter is calculating in the proper way.

 

Thanks!

Attachments
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2021-04-29 02:07 PM . Last Modified: ‎2021-04-29 02:11 PM

0 Likes
2
3242
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-04-29 02:07 PM

Hello @joel_mora_soati,

 

Moved the question to the metering forum

The direct question, how does the ION7650 calculate energy? This is done by integrating the power every second. Have a look at the ION Reference Integrator module for more information.

 

Regarding your equation, there are a few unknowns like what volts mode does the ION7650 meter have, what version of firmware, what template, what setting for the kVA summation. I will assume you have a 4w wye system.

 
In a Wye system, kW total = kW a + kW b + kW c, where kW a ~= Ia * VLN a * PF, since we do not have VLN a, I will estimate VLN A ~= VLL AB / SQRT(3), repeat for each phase. 

 

It looks to me like formula should be /RAIZ(3) and not *RAIZ(3)

 

If you have a Delta system the math would be different as there would be a 2 watt meters. to calculate power.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 3
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2021-04-29 02:07 PM . Last Modified: ‎2021-04-29 02:11 PM

0 Likes
2
3243
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-04-29 02:07 PM

Hello @joel_mora_soati,

 

Moved the question to the metering forum

The direct question, how does the ION7650 calculate energy? This is done by integrating the power every second. Have a look at the ION Reference Integrator module for more information.

 

Regarding your equation, there are a few unknowns like what volts mode does the ION7650 meter have, what version of firmware, what template, what setting for the kVA summation. I will assume you have a 4w wye system.

 
In a Wye system, kW total = kW a + kW b + kW c, where kW a ~= Ia * VLN a * PF, since we do not have VLN a, I will estimate VLN A ~= VLL AB / SQRT(3), repeat for each phase. 

 

It looks to me like formula should be /RAIZ(3) and not *RAIZ(3)

 

If you have a Delta system the math would be different as there would be a 2 watt meters. to calculate power.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
joel_mora_soati
joel_mora_soati
Contributor

Posted: ‎2021-04-29 02:28 PM . Last Modified: ‎2021-04-29 02:30 PM

0 Likes
1
3238
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-04-29 02:28 PM

Thanks @Charles_Murison 

 

It is very clear for me.

 

Refering to the manual calculation, to calculate the active power which of the meter measurements are correct to use:

- Current X Mean (sum the 3 phases) or Current Avg Mean? =>>>>> (Let say this is I in the formula below)
- Voltage X Mean (Average of 3 phases) or Voltage LL Avg Mean? =>>>>(Let say this is V in the formula below)

 

As you said, the proper way to calculate will be:

kW = I*(V/SQRT(3))*PF

 

I really apreciate your help, thanks.

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2021-04-29 03:39 PM

0 Likes
0
3233
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-04-29 03:39 PM

Hello @joel_mora_soati ,

 

The example provided is very simplified, this assumes steady-state, sinusoidal signals. The calculation in general and voltage specifically would depend on what volts mode the system is. Note that the meter likely also logged the power demand. 

 

In general

P = S x PF
where S = V x I, and PF = P / S

P = active power
S = apparent power

Regards,
Charles
L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore