We try to connect the ION meter to SCADA/HMI (ION8800/ION8650) using IEC 61850.
The SCADA use the CID file from meter as reference urcbMMXU01 to urcbMMXU04 but the meter send them with 01 at end. We try to configure the OptFields seqNum to false but when the CID file was upload back to meter we got Invalid CID file.
CID file
<ReportControl bufTime="1000" buffered="false" confRev="1" datSet="MMXU" desc="Unbuffered Measurements Report" indexed="false" intgPd="0" name="urcbMMXU01" rptID="urcbMMXU1">
<Private type="SchneiderElectric-SFT-IsPredefined"/>
<TrgOps dchg="true" dupd="false" period="true" qchg="true"/>
<OptFields configRef="true" dataRef="false" dataSet="true" reasonCode="true" seqNum="true" timeStamp="true"/>
</ReportControl>
Screen shot from scanner the 01 was added monitor from Wireshark also show that the meter add 01. Please advice how the 01 would be eliminated.
Link copied. Please paste this link to share this article on your social media post.
Hello Yut,
I did a bit of investigation and can confirm that the 01 at the end of the name is due to feature described by the IEC 61850 standard, called indexing*. This can be a little misleading as the meter only supports a single subscription to each report but supports 4 "copies" of the report, each with a different name.
* IEC 61850-7-2 Edition 2, Communication networks and systems for power utility automation – Part 7-2: Basic information and
communication structure – Abstract communication service interface(ACSI), 2010.
https://cms-cdn.selinc.com/assets/Literature/Publications/Technical%20Papers/6912_LessonsLearned_BW_... page 4 for more information if desired.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hi Yut,
Can you share which firmware version you are using?
Regards,
Sanjeet
Link copied. Please paste this link to share this article on your social media post.
Hello Yut,
I did a bit of investigation and can confirm that the 01 at the end of the name is due to feature described by the IEC 61850 standard, called indexing*. This can be a little misleading as the meter only supports a single subscription to each report but supports 4 "copies" of the report, each with a different name.
* IEC 61850-7-2 Edition 2, Communication networks and systems for power utility automation – Part 7-2: Basic information and
communication structure – Abstract communication service interface(ACSI), 2010.
https://cms-cdn.selinc.com/assets/Literature/Publications/Technical%20Papers/6912_LessonsLearned_BW_... page 4 for more information if desired.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
The index option in the CET850 was unchecked.
We will do further experiment on both side.
Link copied. Please paste this link to share this article on your social media post.
OK I got it. The RptEna is False. So I have to study CET850 how to set it to True.
Link copied. Please paste this link to share this article on your social media post.
RptEna is true when IEC 61850 client has successfully subscribed to the report on the meter. It is not a variable that can be "set" from outside the meter.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Any suggestion to let the customer be able to get report with their SCADA/HMI ?
Link copied. Please paste this link to share this article on your social media post.
Have the SCADA/HMI use indexing as defined in the standard?!?
I am guessing the name difference is why the client is not getting data from the meter.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Until now no solution for this issue . The customer's SCADA/HMI has no option for handle an extra 01 pad to the name the software read from whatever is in CID file only.
Does anyone on earth has solution ?
Link copied. Please paste this link to share this article on your social media post.
Latest update
Customer can read now in HMI set whatever indicate in CET850 Sevices>Report settings.
Done.