Dear Sir ,
what is the best way to communicate using RS-485 communication with ION 7300 , and please recommend for me the best test equipment to use it for communicate with ION 7330 device
is MOXA USB TO SERIAL (RS-485) is sufficient?
Please note that there is no ethernet interface.
as well what is the best way to communicate with ION 7403, is it Ethernet or Serial and in case of serial please recommend for me the best test equipment to use it for communicate with ION 7403 device
is MOXA USB TO SERIAL (RS-485) is sufficient?
please note that i dont have display for both models , is there any solutions?
Regards ,
Link copied. Please paste this link to share this article on your social media post.
Hello @Anonymous user
ION7300 series, these meters are obsolete. There is limited support. Without Ethernet connection serial is your only option. Without a display may be hard to determine the protocol of the serial ports. Could be ION, could be modbus or others. If ION, you could possibly use the software ION Setup (https://www.se.com/ca/en/download/document/ION_Setup_Latest_Release/)
ION7400 series, recommend using Ethernet. If you connect to the meter directly to a computer and run Wireshark or other packet capture software, you will see the meter send and ARP message that includes it's IP address. From this you can use ION Setup to configure the device.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @Anonymous user
ION7300 series, these meters are obsolete. There is limited support. Without Ethernet connection serial is your only option. Without a display may be hard to determine the protocol of the serial ports. Could be ION, could be modbus or others. If ION, you could possibly use the software ION Setup (https://www.se.com/ca/en/download/document/ION_Setup_Latest_Release/)
ION7400 series, recommend using Ethernet. If you connect to the meter directly to a computer and run Wireshark or other packet capture software, you will see the meter send and ARP message that includes it's IP address. From this you can use ION Setup to configure the device.
Regards,
Charles