Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PM8000 Frequency resolution

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8000 Frequency resolution
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
566
Mehran_Mehrnia
Mehran_Mehrnia Champion
194
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2022-08-28 06:10 PM

0 Likes
6
3638
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-28 06:10 PM

PM8000 Frequency resolution

Hi All,

 

I am trying to determine if the PM8000 meets the requirements of the AEMO Mareket Ancillary Service Specificaiton Verion 7.1 in terms of Frequency resolution for Fast FCAS? Table 4 in 5.3.2  

https://aemo.com.au/-/media/files/stakeholder_consultation/consultations/nem-consultations/2021/mass...

 

As per the attached screen shot the frequency resolution required is <= 0.0025Hz (2.5mHz) for Fast FCAS.

 

If it does not is there a Schneider meter that does?

 

Attachments
Labels
  • Labels:
  • PM8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DanL
DanL Champion
Champion

Posted: ‎2022-08-29 09:47 AM

2 Likes
2
3617
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-29 09:47 AM

Yes, the frequency registers have better than 2.5mHz precision on the PM8000 (when read or recorded in Float32 format).

The PM8000 uses a 40MHz clock to measure the periods of the zero crossings of the fundamental voltage.

 

Model ION Module ION Register Measurement window Update period Standard Compliance Claimed Accuracy Precision
PM8000 Power Quality Aggregator Power Frequency 10 s 10 s

IEC61000-4-30

Class S*

+/-10mHz

< 0.01mHz

(7 digits)

PM8000 Power Meter Module Freq 1 s 1 s

IEC61557-12

CL,02

+/-0.02% = +/-10mHz

< 0.01mHz

(7 digits)

PM8000 HS Power Meter Module HS Freq 1 cycle 1/2 cycle    

< 0.1mHz

(6 digits)

 

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 6
DanL
DanL Champion
Champion

Posted: ‎2022-08-29 09:47 AM

2 Likes
2
3618
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-29 09:47 AM

Yes, the frequency registers have better than 2.5mHz precision on the PM8000 (when read or recorded in Float32 format).

The PM8000 uses a 40MHz clock to measure the periods of the zero crossings of the fundamental voltage.

 

Model ION Module ION Register Measurement window Update period Standard Compliance Claimed Accuracy Precision
PM8000 Power Quality Aggregator Power Frequency 10 s 10 s

IEC61000-4-30

Class S*

+/-10mHz

< 0.01mHz

(7 digits)

PM8000 Power Meter Module Freq 1 s 1 s

IEC61557-12

CL,02

+/-0.02% = +/-10mHz

< 0.01mHz

(7 digits)

PM8000 HS Power Meter Module HS Freq 1 cycle 1/2 cycle    

< 0.1mHz

(6 digits)

 

Tags (1)
  • Tags:
  • english
Reply
Anonymous user
Not applicable

Posted: ‎2022-08-29 03:58 PM

0 Likes
1
3609
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-29 03:58 PM

Hi Dan,

 

Thanks for that. Just what I needed.

 

I was wondering where you sourced the information from? Is there any official Schneider documentation with that written down?

I will likely need to show the client that the meter satifies the requirement. If it is not in official documentation an email from local Schneider team will hopefully suffice.

 

Thanks again.

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2022-08-30 09:37 AM

0 Likes
0
3585
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-30 09:37 AM

Hello @Anonymous user 

 

Standard Compliance and Claimed Accuracy can be found in the technical datasheet
https://www.se.com/ca/en/download/document/PLSED310058EN_Web/

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Kamal_Kant
Kamal_Kant Explorer
Explorer

Posted: ‎2025-07-23 12:22 AM

0 Likes
2
1257
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-23 12:22 AM

Hello Dan and Charles,

Thank you for your responses.

I’m also looking for a supporting document to share with our customer in Australia. I tried accessing the details through the link you previously provided, but it appears to no longer be valid. Could you please assist with an updated link or share the relevant document directly?

Thank you in advance.

Best regards,
Kamal Kant

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2025-07-23 11:06 AM

1 Like
1
1252
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-23 11:06 AM

Hello @Kamal_Kant ,

 

https://download.schneider-electric.com/files?p_Doc_Ref=PLSED310058EN&p_enDocType=Other+technical+gu... is a link that works for me. Another option would be to go to se.com and search for "PLSED310058EN" (without quotes).


Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Kamal_Kant
Kamal_Kant Explorer
Explorer

Posted: ‎2025-07-23 04:10 PM

0 Likes
0
1248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-23 04:10 PM

Hi Charles,

Thank you for the new link, it works.

 

Best Regards,

Kamal Kant

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore