Hello everyone,
Wonder what the max number of concurrent TCP (more specified ModTCP) connections is supported by HDPM6000 head unit? I have been going through the technical data sheets, but have not found the answer yet.
Regards,
Link copied. Please paste this link to share this article on your social media post.
Hello @Yu_Diao
The next revision of the technical datasheet should provide this information. Currently the maximum number of modbus connections is 10.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Charles,
Thanks! Very useful info and it helps us to set up proper system architecture.
Regards,