Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

IEEE 519 PME Reports shows Aggregates0% values Very Short Time Voltage Distortion Compliance - 99th Percentile

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • IEEE 519 PME Reports shows Aggregates0% values Very Short Time Voltage Distortion Compliance - 99th Percentile
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Jagadish
Jagadish
Explorer

Posted: ‎2024-07-03 10:37 AM

0 Likes
3
2031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-03 10:37 AM

IEEE 519 PME Reports shows Aggregates0% values Very Short Time Voltage Distortion Compliance - 99th Percentile

I have been looking for IEEE519 reports from PME for PM8000 device,report generated for Last 7 days.but not getting 0% aggregate value on Individual & THD. and V1,V2,V3 values are blank for Very Short Time Voltage Distortion Compliance - 99th Percentile for Non compliance days.

Similar results for veryshort time current harmonics 99th percentile too.

 

Isc/IL = 10 Individual Harmonic Order (Odd) TDD (%)
Ratio Window Limit (0 - 20) <11 11≤h<17 17≤h<23 23≤h<35 35≤h
IEEE 519 Limit (%) 8 4 3 1.2 0.6 10
Non-compliant 3-second Days 2 2
Total Days 7
Compliance FAIL FAIL
Very Short Time Current Distortion Compliance - Non Compliant Days
Individual Harmonics TDD Limit - 10
Date Aggregate I1 I2 I3 Aggregate I1 I2 I3
6/30/2024 0.00% 0.00%
7/1/2024 0.00% 0.00%

Labels
  • Labels:
  • ION Setup
  • PM8000
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2024-07-12 09:28 AM

1 Like
0
1920
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-12 09:28 AM

Hello @Jagadish ,

 

PME does not calculates the aggregate % Non compliance to 99th percentile daily 3sec from Individual voltage /current components % Non compliance to 99th percentile. 
In the meter there are many counts getting incremented and counted.
A) Valid intervals
B) Intervals on V1/V2/V3, I1/I2,I3 as well as a count if any V1/V2/V3 or I1,I2,I3 where individual Harmonics exceed limits (8 different counters).
C) Intervals on V1/V2/V3, I1/I2,I3 as well as a count if any V1/V2/V3 or I1,I2,I3 where THD exceed limits (8 different counters).

D) Invalid intervals

The only calculation that PME does is 1-(X/Y) where X and Y are different counts from Meter
ex 1-(5505/28224) = 0.80495 = 80.50%
You cannot calculate aggregate from individual phases. What you can get is the possible range.
100 - (100-V1) - (100-V2) - (100-V3) <= Aggregate <= min(V1,V2,V3)

 

An invalid interval is where where there is a PQ event, sag/swell or interruption.

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 3
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2024-07-04 09:31 AM

0 Likes
0
2006
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-04 09:31 AM

Hello @Jagadish ,

 

I am sorry I am having a little trouble understanding your post. Would be good to determine what is available where in your system. For the IEEE519 reports in PME. There are different reports for different versions of the IEEE519 standard. Different templates on the meter were designed for different versions of the standard. The meter has a number of onboard logs that are then feed into PME database for the report. The report is looking for very specific measurement names. Different versions of the report use different measurement names. 

I am going to assume you are using a meter with V2.1.0 or later version of firmware with the default template.
A) Is the IEEE519 enabled? and the correct settings applied to the meter?

Charles_Murison_0-1720109569390.png

B) Is the meter logging values for the desired measurements?

Charles_Murison_1-1720109772340.pngCharles_Murison_2-1720110533007.png

C) Does the logged values get into PME database?

D) Are you using the correct report?

First step for me would be to confirm that you are logging the desired values. Note that PM8000 Standard does not have enough data recorders to log all possible individual harmonic information (I1 H2, I1 H3 etc.) the report can use.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Jagadish
Jagadish
Explorer

Posted: ‎2024-07-12 05:48 AM

0 Likes
1
1933
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-12 05:48 AM

Hello @Charles_Murison 

Thanks for the information shared. Now I am getting values for IEEE519 Compliance by simulating Harmonic injection using secondary injection kit.

But how do PME Calculates the aggregate % Non compliance to 99th percentile daily 3sec from Individual voltage /current components % Non compliance to 99th percentile.

Hi attaching both from device webpage & PME ResultsDevice webpage1Device webpage1

 

Device webpage2Device webpage2

 

PME CompliancePME Compliance

 Whats that "Invalid Interval". I have observed "Valid Intervals" are incrementing in each 3sec.

Thanks

Jagadish

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2024-07-12 09:28 AM

1 Like
0
1920
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-12 09:28 AM

Hello @Jagadish ,

 

PME does not calculates the aggregate % Non compliance to 99th percentile daily 3sec from Individual voltage /current components % Non compliance to 99th percentile. 
In the meter there are many counts getting incremented and counted.
A) Valid intervals
B) Intervals on V1/V2/V3, I1/I2,I3 as well as a count if any V1/V2/V3 or I1,I2,I3 where individual Harmonics exceed limits (8 different counters).
C) Intervals on V1/V2/V3, I1/I2,I3 as well as a count if any V1/V2/V3 or I1,I2,I3 where THD exceed limits (8 different counters).

D) Invalid intervals

The only calculation that PME does is 1-(X/Y) where X and Y are different counts from Meter
ex 1-(5505/28224) = 0.80495 = 80.50%
You cannot calculate aggregate from individual phases. What you can get is the possible range.
100 - (100-V1) - (100-V2) - (100-V3) <= Aggregate <= min(V1,V2,V3)

 

An invalid interval is where where there is a PQ event, sag/swell or interruption.

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore