Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Link copied. Please paste this link to share this article on your social media post.
Hi,
I am looking to change the update rate of the High Speed ION Modules on one of the ION 9000s that I am working on. By default it updates the readings every half of a cycle (10ms) and I am trying to set it at 20ms. Is it possible? How do I change this?
Thank you,
Jonathan.
Link copied. Please paste this link to share this article on your social media post.
Hello @jonathanzamban ,
The ION module speeds are either high speed (half cycle) slow speed (1 second) or event driven. There is no way to select an update rate. What module are you working with and why do you want the update to be every 20 ms?
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @jonathanzamban ,
The ION module speeds are either high speed (half cycle) slow speed (1 second) or event driven. There is no way to select an update rate. What module are you working with and why do you want the update to be every 20 ms?
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hi @Charles_Murison,
Thanks for clarifying.
I am testing a framework with the High-Speed measurements (Voltage, Current, Frequency, etc.) and I am looking to log them for a short period with 20ms space between each log.
But, I will try to overcome this with a 20ms timer trigger for each record.
Thanks for your help,
Jonathan.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.