Hi,
We intend to get slow AND also fast measurements at our ION8650. We need request this data at real time and using modbus TCP table.
We configure a PLC to act as modbus master and request data each 60ms. So we are able to read VLL avg scaled(address-40184) and kw tot scaled (address-40204), although the meter answer each of our request this values only update at each 1s.
This measurement, at 1s rate, is very good for revenenue measurements because don`t show noise. However we would like to know how to read faster measurements too, even with noise.
I read the manual a lot and sounds that 8650 allow to measure1/2 cycle (instantaneous measurements). This fast measurement is allow to be request at modbus interface? How to configure 8650 to do that?
Link copied. Please paste this link to share this article on your social media post.
Hello @rodrigorpgsc ,
You are correct that the ION8650 meter does have some modules that update at a 1/2 cycle rate and other modules that update at 1 second and very few that can be either. The modbus slave modules (used for modbus communications) is a module that only updates once a second regardless of what inputs are connected. There is no way to retrieve data from the meter via modbus any faster than once a second.
The protocol DNP can update at the 1/2 cycle rate, but only for a few measurements as configuring the module for 1/2 cycle uses a significate amount of CPU power.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello Rodrigo,
Using ION Setup DNP wizard to setup the DNP could work but may hide some elements from you. I would put meter into advanced mode, add the module, link registers and configure registers manually. This is not a simple task which is why the wizard in ION Setup exists.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @rodrigorpgsc ,
You are correct that the ION8650 meter does have some modules that update at a 1/2 cycle rate and other modules that update at 1 second and very few that can be either. The modbus slave modules (used for modbus communications) is a module that only updates once a second regardless of what inputs are connected. There is no way to retrieve data from the meter via modbus any faster than once a second.
The protocol DNP can update at the 1/2 cycle rate, but only for a few measurements as configuring the module for 1/2 cycle uses a significate amount of CPU power.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Charles,
Thanks!
We`ll try to request using DNP protocol for 1/2 cycle.
Link copied. Please paste this link to share this article on your social media post.
5 variable using 1/2 cycle update time and DNP3 sound ok or is too much for CPU ?
Link copied. Please paste this link to share this article on your social media post.
Hello @rodrigorpgsc ,
The DNP module itself is not a standalone item. The total CPU usage is also dependent on the rest of the framework on the meter. For example if you do not need EN50160 there is a bit of CPU usage you could save CPU "space" by removing the modules that support EN50160.
DNP modules can have up to 4 inputs. If trimming down to 4 measurements is an option that would be easiest. If 5 measurements are a requirement then 2 DNP modules needed. The DNP module at 1/2 cycle update times will use the same CPU usage with 1 measurement linked as 4. Just to keep this in mind when selecting measurements.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hi Charles,
Thanks (a lot) for your patience
I logging at 8650, using SCH ION setup, and find 34 (`slow`) points at standard DNP map, so the standard map is using 9 dnp modules by standard, don`t?If I don`t erase the default and insert 5 points I`ll use 10 dnp modules, don`t?
The rigth place to configure the export of HS is at (I attach a screnshot)
Ion setup->3rd party comm->DNP map setup ->dnp register ->Parameter selection
?
I intend to select a HF variable, ex: HS PF lead tot, and put at map to allow my PLC to begin request to request this fast variable
Link copied. Please paste this link to share this article on your social media post.
Hello Rodrigo,
Using ION Setup DNP wizard to setup the DNP could work but may hide some elements from you. I would put meter into advanced mode, add the module, link registers and configure registers manually. This is not a simple task which is why the wizard in ION Setup exists.
Regards,
Charles