Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Get this new approach to evaluating Voltage Sags

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Get this new approach to evaluating Voltage Sags
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Related Products
product field
Schneider Electric
PowerLogic DVR

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Sreemant_Roy
Sreemant_Roy Contributor
Contributor

Posted: ‎2022-09-23 06:34 AM . Last Modified: ‎2022-09-27 06:22 AM

2 Likes
2
2324
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-23 06:34 AM

Get this new approach to evaluating Voltage Sags

 

Sharing extracts from a recent Technical Article authored by Jon Bickel, P.E., Power Applications, Schneider Electric.

 

The paper discusses the impacts of voltage events such as sags / dips and short interruptions related to power quality issues. Whether originating at the utility or inside an end user’s facility, it is important to understand operational impacts, and to differentiate nuisance events from disruptive events. Ascertaining the level of impact from voltage events allows easier prioritizing of alarms, creating and trending historical effects from disruptive perturbations, and determining locations and sizes of mitigation equipment.

 

Traditionally mid/high-end metering devices have had the ability to capture short duration rms variations such as voltage sags/dips for decades. These devices typically provide a time-series image of voltage perturbations (e.g., sags/dips) that include all metered voltage and current phases.

When analyzing voltage events, there are several questions to be answered including:

 

What type of voltage event was it?

How long did the voltage event last?

Was the source of the voltage event internal or external 

What caused the voltage event?

Is this voltage event a reoccurring issue?

and most importantly…WAS MY OPERATION IMPACTED?

 

The figure below illustrates the normal voltage range (shaded area) that is bounded by an upper and lower alarm threshold. The rated or nominal voltage is also shown.

 

When the measured voltage level goes below the lower alarm threshold (e.g., see the voltage event shown in the figure below) an alarm will be initiated by the metering device.

 

Sreemant_Roy_0-1663939192938.png

 

 

The event alarm data typically includes information such as worst magnitude of the event, duration of the event, start time and date of the event, alarm type, and (depending on the device) a waveform capture of the three-phase voltages and currents during the event. Each of these event parameters provide important clues to troubleshoot the voltage event and answer the questions listed above.

 

 

However, one very important question is not directly addressed: Did the voltage event impact the load? To determine whether the voltage event resulted in a load impact, a more thorough analysis of the waveform capture must be performed.

 

Let’s look at Load loss

Figure – 1 below illustrate a voltage sag event on a three-phase, 60 Hertz, 347/600-volt wye-configured system. The event shown in this example appears to have been caused by an upstream fault.

Sreemant_Roy_1-1663939193108.png

 

Figures 2&3 below are derived from the event waveform data captured in the figure -1 above. The voltage event lasted approximately 11 cycles (or about 180 milliseconds) in duration, and the worst-case voltage deviation during the event was approximately 53% of the nominal voltage (or 184 volts) on Phase C as shown in figure 2 (rms voltage) below.

Sreemant_Roy_2-1663939193263.png

 

Figure 3 illustrates the rms real power data throughout the voltage event and is the data with the most relevance for troubleshooting the event’s impact. Before the event began (pre-event), the total real power consumed by the downstream load(s) was approximately 1,458kW.

The voltage event began when t ≈ 0.07 seconds and is assumed to have concluded once the voltage recovered to its normal operating range (t ≈ 0.26 seconds). Upon the conclusion of the event (i.e., post-event), the total real power consumed by the downstream load(s) was approximately 544kW.

Therefore, the pre-event versus post-event total power flow to the load(s) decreased by about 914kW (or 63%) as a result of the voltage sag event.

The conclusion is the voltage event caused 914kW (or 63%) of load to de-energize (drop offline), likely resulting in a significant impact to the facility’s operation.

 

Conclusion

Globally, voltage events such as sags/dips and short interruptions are the biggest contributor to losses related to power quality issues. Voltage events can be external (e.g., originate on the utility) or internal (e.g., originate inside the end-user’s facility), anticipated (e.g., starting a large load) or unpredictable (e.g., a system fault), impactful (e.g., loads de-energize) or inconsequential (e.g., system continues to operate with no issues).

 

Recognizing the existence of voltage perturbations and characterizing their properties (e.g, worst magnitude, duration, etc.) is not sufficient; it is important to understand the operational impact to differentiate nuisance events from disruptive events.

 

Ascertaining the level of "Operational impact" from voltage events (regardless of their origin) facilitates easier prioritizing and filtering metering system alarms, creating and trending historical effects from disruptive perturbations, and determining locations and sizes of mitigation equipment like Schneider Electric’s PowerLogic Dynamic Voltage Restorer ( DVR), is the "Key" to resolving a client's PQ Challenge.

 

Discover more about PowerLogic DVR HERE

 

Sreemant Roy
Product Owner - Active Power Quality Solutions ( AccuSine & DVR's )
  • Thumbnail of PowerLogic DVR
    Schneider Electric
    PowerLogic DVR
View products (1)
Labels
  • Labels:
  • Power Quality
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Sepehr_Zarrabi
Sepehr_Zarrabi Troubleshooter
Troubleshooter

Posted: ‎2022-09-23 11:26 AM

0 Likes
0
2242
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-23 11:26 AM

Great article, which makes a very good point: regardless of the severity of the event, how did the loads / processes get impacted?

 

The "load loss" calculation discussed in this article is performed automatically by the PME (Power Monitoring Expert) software (image below).

 

Annotation 2022-09-23 112542.png

 

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 2
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2022-09-23 08:58 AM

1 Like
0
2304
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-23 08:58 AM

Thank you for sharing this information.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Sepehr_Zarrabi
Sepehr_Zarrabi Troubleshooter
Troubleshooter

Posted: ‎2022-09-23 11:26 AM

0 Likes
0
2242
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-23 11:26 AM

Great article, which makes a very good point: regardless of the severity of the event, how did the loads / processes get impacted?

 

The "load loss" calculation discussed in this article is performed automatically by the PME (Power Monitoring Expert) software (image below).

 

Annotation 2022-09-23 112542.png

 

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore