Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PM8000 as a data logger

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8000 as a data logger
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
581
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Grant_IPACS
Grant_IPACS
Mentor

Posted: ‎2018-12-07 12:48 AM

0 Likes
4
4558
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-12-07 12:48 AM

PM8000 as a data logger

Hi All,

 

We have a client who suspects issues with harminics on large mechanical plant on site.

We have been seeing them as a propect for normal energy metering retrofit & PME for some time now, but nothing eventuated yet.

 

They now believe they may have issues with underperforming passive filters...

 

In lieu of hiring high speed waveform & data loggers they are now asking us if fitting PM8000's can help identify their issues. (and they then keep them permantly afterwards)  so they can get the right accusine harmonic filter or similar.

 

My thougts are that it would not be my first choice solution, as i would rather see all the waveforms through start-up and continious run & load step changes over a week or so, whereas the PM8000 will only log waveforms by exception / event, however we could get some interval log data out that would be useful.

 

Would appreciate anyones opinion or similar experiences.

 

Reagrds

 

Grant

Regards

Grant
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2018-12-10 03:14 PM

1 Like
3
4550
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-12-10 03:14 PM

Hi Grant,

The  PM8000 has enough available additional data recorders and waveform recorders perform as a data logger,  To configure it to do a specific form of data logging will require knowledge of ION Meter Module programming generally done with the Designer app in PME.
Triggering the recorders could be done via a physical signal ihnto one of the PM8000 digital inputs or by monitoring for a change of state such as an increase in current or power.  

As of the next firmware release (V2.0 1st qtr 2019) the PM8000 will support the "burst mode" recording of the data recorder which allows for pre/post trigger  numeric data recording.  Inputs to such a recorder could be the voltage harmonic values etc.  The same trigger to cause a wave form recorder to capture voltage/current waveforms at an appropriate sampling rate.

Analysis of captured data can be done in PME9,0.

Regards,

Jim

 

See Answer In Context

Reply
Replies 4
Anonymous user
Not applicable

Posted: ‎2018-12-10 03:14 PM

1 Like
3
4550
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-12-10 03:14 PM

Hi Grant,

The  PM8000 has enough available additional data recorders and waveform recorders perform as a data logger,  To configure it to do a specific form of data logging will require knowledge of ION Meter Module programming generally done with the Designer app in PME.
Triggering the recorders could be done via a physical signal ihnto one of the PM8000 digital inputs or by monitoring for a change of state such as an increase in current or power.  

As of the next firmware release (V2.0 1st qtr 2019) the PM8000 will support the "burst mode" recording of the data recorder which allows for pre/post trigger  numeric data recording.  Inputs to such a recorder could be the voltage harmonic values etc.  The same trigger to cause a wave form recorder to capture voltage/current waveforms at an appropriate sampling rate.

Analysis of captured data can be done in PME9,0.

Regards,

Jim

 

Reply
Mike78
Mike78
Explorer

Posted: ‎2022-09-19 10:03 AM

0 Likes
2
4187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-19 10:03 AM

Hello Jim

 

he have the same issue.

 

we need get the Voltage/Current waveform when we get a event in grid.

 

like:

 

I>>

I<<

U>>

U<<

 

This is swag a swell in voltage and current, like you can see in attached picture

 

However, we need to connect the trips from switch-gear protection relay to start the waveform recording when we have trips in relay and also when the switch opens.

 

The trips could be:

 

f<<

f>>

Uo>>

I0>>

S>> 

 

Do you have an example to configure the PM8000 to receive triggers from inputs and that we can implemented the waveform logging (before and after event)?

 

Thank you

 

Miguel Santos 

Attachments
Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2022-09-19 11:34 AM

0 Likes
1
4181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-19 11:34 AM

Hello @Mike78 ,

 

The world of ION is highly customizable. Likely you would want to use a pulse merge module to combine all possible triggers, then feed this to the waveform recorder. For example, digital input modules have a trigger pulse output that can be used to trigger a waveform. The inputs from multiple digital inputs would be feed into a pulse merge module and the output of the pulse merge module feed into the existing waveform recorder framework. 

 

Regards,

Charles

 

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Mike78
Mike78
Explorer

Posted: ‎2022-09-21 10:45 AM

1 Like
0
4138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-21 10:45 AM

Hello Charles

 

Thank you for you reply

 

I already did it using designer (PME application). A very tricky application but functional.

 

DesignerConf.png

 

seems to be work.

 

Miguel Santos

 

 

 

Attachments
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore