Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

EM4200 Live Data Table

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Re: EM4200 Live Data Table
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
484
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
89
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
michael_franz
Admiral michael_franz
Admiral

Posted: ‎2017-07-14 06:26 AM . Last Modified: ‎2020-04-22 01:15 AM

0 Likes
3
1818
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-07-14 06:26 AM

EM4200 Live Data Table

ION Setup has an entry for this meter but appears to be lacking live data table for this type.

 

This is .16xxxx that we had believed to be the newest.

EM4200.jpg

 

 

Found .17xxxx and at least we do not get the "no tables found" error.  Won't know if this is the

fix until we can connect to a meters.

Attachments
Labels
  • Labels:
  • ION Setup
Tags (7)
  • Tags:
  • data
  • em4200
  • ion setup
  • live data
  • meter
  • missing_values
  • table
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2017-07-18 12:04 PM

1 Like
1
1793
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-07-18 12:04 PM

I believe what is happening is that ION Setup is presently trying to use the wrong folder names since the EM4200 is a somewhat new product.  It is automatically talking to the device and instead of picking the "EM4235" folder which is what ION Setup installed, it is selecting "Enhanced" (which is left over from the older Enercept implementation).  Likewise the "EM4236" is selecting the "Basic" instead.

For now you should can select the Display tab and manually select the proper model (make sure either the EM4235 or EM4236 is highlighted) or if that doesn't work, using Windows Explorer, create copies of the existing folders and rename them appropriately (ex. copy of the EM4235 folder call it "Enhanced").

I will try and update ION Setup to select the proper folders in the next release.

See Answer In Context

Reply
Replies 3
michael_franz
Admiral michael_franz
Admiral

Posted: ‎2017-07-17 07:38 AM

0 Likes
0
1793
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-07-17 07:38 AM

TEAM:

No takers on this???  ION Setup is an important tool.  We need those tables.

Thanks,

Michael Franz

Reply
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2017-07-18 12:04 PM

1 Like
1
1794
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-07-18 12:04 PM

I believe what is happening is that ION Setup is presently trying to use the wrong folder names since the EM4200 is a somewhat new product.  It is automatically talking to the device and instead of picking the "EM4235" folder which is what ION Setup installed, it is selecting "Enhanced" (which is left over from the older Enercept implementation).  Likewise the "EM4236" is selecting the "Basic" instead.

For now you should can select the Display tab and manually select the proper model (make sure either the EM4235 or EM4236 is highlighted) or if that doesn't work, using Windows Explorer, create copies of the existing folders and rename them appropriately (ex. copy of the EM4235 folder call it "Enhanced").

I will try and update ION Setup to select the proper folders in the next release.

Reply
michael_franz
Admiral michael_franz
Admiral

Posted: ‎2017-07-18 12:08 PM

0 Likes
0
1793
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-07-18 12:08 PM

Robert Lee:

I had 3.0.16xxxxx that had claimed to be the newest.  Got a link for 3.0.17xxxxx

that looks like it will work.

Thanks,

Michael

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of