Hi, All
When I add a modbus serial device to a site, the device name cannot start with numbers, is that right? There is a BCPM on site which I want to configure, the label of BCPM is A5-PDU-37B, I just want to quickly configure it, so I put 37B as the device name, then I found the drop down box of device type doesn't work and the OK buttons is greyed out.
Thanks,
James Rong
Link copied. Please paste this link to share this article on your social media post.
James,
It has to begin with a letter. BTW, u can only use letter, space. It will convert underline "_" to space automatically without a warning. It does not take "-", so u cannot do "pdu-5A".
It has been like this for a long time, at least back to V2.2, but it does not really bother me these years, as I just use it during commission phase, so I just went with it. -:)
Regards
Sent from my mobile device.
Link copied. Please paste this link to share this article on your social media post.
First character must be letter ( Space, underline, or special character *, ^...is not allowable ).