Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Link copied. Please paste this link to share this article on your social media post.
Hello,
I have a question regarding the PM5560 meter and DNP3.
We want to see the analog values in 16-bit floating point function or scaled. The User manual on page 113 mentions that 16-bit floating is supported.
In addition to that, the function Data poll Class123 does not refresh after 3 seconds in the SCADA. The integrity data poll works fine. It takes about 1 minute to refresh. Does anyone know if this is how it's supposed to work? Any advise is appreciated.
Link copied. Please paste this link to share this article on your social media post.
Hello @Robert_MDIC ,
Does https://www.productinfo.schneider-electric.com/pm5500/595e2aa946e0fb0001f715da/PM5500%20user%20manua... provide some of the information you need?
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @Robert_MDIC ,
Does https://www.productinfo.schneider-electric.com/pm5500/595e2aa946e0fb0001f715da/PM5500%20user%20manua... provide some of the information you need?
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Thanks, @Charles_Murison Yes, that table helps to visualize all the pre defined objects in the PM5500 DNP3 protocol.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.