Current probe option

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
Yut
Captain
Captain
0 Likes
6
1364

Current probe option

Is there any document describe what current channel the option be applied to ?

Customer thought the option can be used with I4 they connected probe to I4 to measure Neutral current from existing CT sec.

I understand from the beginning of ION76xx/75xx current option that the probes are for I1 I2 and I3 only. Is there any update on the latest version of ION7650 ?

See screen capture they connected I4 to r phase.

Vector Diagram.jpg

Tags (1)

Accepted Solutions
DanL
Commander Commander
Commander
0 Likes
0
1348

Re: Current probe option

Hello,

I'm pretty sure I remember there is (or was) an option to order 0, 3, or 5 probes with the ION7650 NICP option.

Because the meter only computes power from 3 of the phases, only I1(Ir), I2(Iy), and I3(Ib) can have phase calibration.

Yes, I4 and I5 can be used to measure the current for any use the customer may have (each with their own CT ratio).

 

I'm not sure what you mean regarding "the latest version of ION7650"? Do you asking about the ION9000 Low Voltage Current Sensor hardware model?

 

PS. The phasor diagram indicates the meter is wired for 3WIRE Delta but the angles between the current phases is significantly unbalanced. The phase angle imbalance suggests that this 3wire system either has unbalanced single phase (line-to-line) loads, or perhaps there is a wiring error. Depending on the power quadrant expected, most likely either:

1. Iy and Ib are inverted

2. only Ir is inverted

See Answer In Context

Tags (1)
6 Replies 6
Charles_Murison
Picard Picard
Picard
0 Likes
4
1352

Re: Current probe option

@DanL do you know if the current probe option for ION7650 has changed to include I4 input?

L4 Prime for Advanced metering and Utilities
Tags (1)
DanL
Commander Commander
Commander
0 Likes
0
1349

Re: Current probe option

Hello,

I'm pretty sure I remember there is (or was) an option to order 0, 3, or 5 probes with the ION7650 NICP option.

Because the meter only computes power from 3 of the phases, only I1(Ir), I2(Iy), and I3(Ib) can have phase calibration.

Yes, I4 and I5 can be used to measure the current for any use the customer may have (each with their own CT ratio).

 

I'm not sure what you mean regarding "the latest version of ION7650"? Do you asking about the ION9000 Low Voltage Current Sensor hardware model?

 

PS. The phasor diagram indicates the meter is wired for 3WIRE Delta but the angles between the current phases is significantly unbalanced. The phase angle imbalance suggests that this 3wire system either has unbalanced single phase (line-to-line) loads, or perhaps there is a wiring error. Depending on the power quadrant expected, most likely either:

1. Iy and Ib are inverted

2. only Ir is inverted

Tags (1)
DanL
Commander Commander
Commander
0 Likes
3
1347

Re: Current probe option

All options of the ION7650 include both I4 and I5 inputs on the meter. I believe for the low voltage current probe option, there are options for 0, 3, and 5 probes. And of course the customer can order probes separately to use as they want.

Tags (1)
Yut
Captain
Captain
0 Likes
2
1342

Re: Current probe option

So I will check the order option. Those meters were the last lot before the ION9000 were release.

 

Tags (1)
Charles_Murison
Picard Picard
Picard
1
1339

Re: Current probe option

Helo Yut,

 

What I believe Dan is saying is that the meter came with the option to order probes with the meter or supply your own probes. He is not talking about what options are inside the meter.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
Yut
Captain
Captain
0 Likes
0
1336

Re: Current probe option

I checked the order option the current input was G means 3 voltage input with 3 current clamps. 

Thank you very much everyone.