Dear experts,
I have a costumer requirement, who wants to edit the template of all his ION8650 meters (at least 20 meters), he want to save Vln by default, is there any option to do that without editing each meter template one by one?
When I ckeck the ION 8650 Template I found just data related to Vll
What should I do ?
Link copied. Please paste this link to share this article on your social media post.
The following datarecorders log VLN rms values on the 8650A & 8650B frameworks:
#38: 4-30 3s RMS Log
#16: 4-30 10mRMS Log
#37: 4-30 2hrRMS Log
#32: EN50160 Prm-f/V
Hope this helps.
Link copied. Please paste this link to share this article on your social media post.
Hello @JuanMQT
I moved your post to the power metering forum. I would ask future metering questions here.
As for the meter programming, yes you will need to do this one meter as a time. However there multiple ways to do this and some are faster than others.
For example you can add an additional data recorder, assuming meter has module space available, with links to desired measurements, this can be then saved as a framelet. also know as partial framework. Then you can paste this framelet onto the additional meters either with Designer in PME or ION Setup. Other options include creating the entire framework file usually as dcf and pasting this on the meter additional meters. Doing this will remove any existing logging on the meter.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
The following datarecorders log VLN rms values on the 8650A & 8650B frameworks:
#38: 4-30 3s RMS Log
#16: 4-30 10mRMS Log
#37: 4-30 2hrRMS Log
#32: EN50160 Prm-f/V
Hope this helps.