Current probe option

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Current probe option
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
478
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
89
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Yut
Captain Yut
Captain

Posted: ‎2020-11-16 01:55 AM . Last Modified: ‎2024-01-30 05:14 AM

0 Likes
6
2822
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-11-16 01:55 AM

Current probe option

Is there any document describe what current channel the option be applied to ?

Customer thought the option can be used with I4 they connected probe to I4 to measure Neutral current from existing CT sec.

I understand from the beginning of ION76xx/75xx current option that the probes are for I1 I2 and I3 only. Is there any update on the latest version of ION7650 ?

See screen capture they connected I4 to r phase.

Vector Diagram.jpg

Labels
  • Labels:
  • ION7000
  • ION9000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DanL
Captain DanL Captain
Captain

Posted: ‎2020-11-20 11:01 AM

0 Likes
0
2806
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-11-20 11:01 AM

Hello,

I'm pretty sure I remember there is (or was) an option to order 0, 3, or 5 probes with the ION7650 NICP option.

Because the meter only computes power from 3 of the phases, only I1(Ir), I2(Iy), and I3(Ib) can have phase calibration.

Yes, I4 and I5 can be used to measure the current for any use the customer may have (each with their own CT ratio).

 

I'm not sure what you mean regarding "the latest version of ION7650"? Do you asking about the ION9000 Low Voltage Current Sensor hardware model?

 

PS. The phasor diagram indicates the meter is wired for 3WIRE Delta but the angles between the current phases is significantly unbalanced. The phase angle imbalance suggests that this 3wire system either has unbalanced single phase (line-to-line) loads, or perhaps there is a wiring error. Depending on the power quadrant expected, most likely either:

1. Iy and Ib are inverted

2. only Ir is inverted

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 6
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2020-11-20 09:34 AM

0 Likes
4
2810
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-11-20 09:34 AM

@DanL do you know if the current probe option for ION7650 has changed to include I4 input?

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2020-11-20 11:01 AM

0 Likes
0
2807
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-11-20 11:01 AM

Hello,

I'm pretty sure I remember there is (or was) an option to order 0, 3, or 5 probes with the ION7650 NICP option.

Because the meter only computes power from 3 of the phases, only I1(Ir), I2(Iy), and I3(Ib) can have phase calibration.

Yes, I4 and I5 can be used to measure the current for any use the customer may have (each with their own CT ratio).

 

I'm not sure what you mean regarding "the latest version of ION7650"? Do you asking about the ION9000 Low Voltage Current Sensor hardware model?

 

PS. The phasor diagram indicates the meter is wired for 3WIRE Delta but the angles between the current phases is significantly unbalanced. The phase angle imbalance suggests that this 3wire system either has unbalanced single phase (line-to-line) loads, or perhaps there is a wiring error. Depending on the power quadrant expected, most likely either:

1. Iy and Ib are inverted

2. only Ir is inverted

Tags (1)
  • Tags:
  • english
Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2020-11-20 11:03 AM

0 Likes
3
2805
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-11-20 11:03 AM

All options of the ION7650 include both I4 and I5 inputs on the meter. I believe for the low voltage current probe option, there are options for 0, 3, and 5 probes. And of course the customer can order probes separately to use as they want.

Tags (1)
  • Tags:
  • english
Reply
Yut
Captain Yut
Captain

Posted: ‎2020-11-22 11:09 PM

0 Likes
2
2800
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-11-22 11:09 PM

So I will check the order option. Those meters were the last lot before the ION9000 were release.

 

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2020-11-23 09:49 AM

1 Like
1
2797
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-11-23 09:49 AM

Helo Yut,

 

What I believe Dan is saying is that the meter came with the option to order probes with the meter or supply your own probes. He is not talking about what options are inside the meter.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Yut
Captain Yut
Captain

Posted: ‎2020-11-23 10:39 PM

0 Likes
0
2794
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-11-23 10:39 PM

I checked the order option the current input was G means 3 voltage input with 3 current clamps. 

Thank you very much everyone.

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of