2024-03-2508:32 AM
Hi @MartinRichnak As already mention in 'Direct connect voltage limits' section of PM5500 user guide: "The meter's voltage measurement inputs are rated by the manufacturer for up to 400 V L-N / 690 V L-L. However, the maximum voltage allowed for direct connection may be lower, depending on the local electrical codes and regulations." NOTE: Use a 500 mA fuse or a circuit breaker for the meter voltage input terminals.
Best Regards, -Mehran L3 Expert Technical Support Specialist