Config communication PM8000

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
SESA_B
Lt. Commander Lt. Commander
Lt. Commander
19
1856

Config communication PM8000

Hi teams,

 

I have concern, i want configure in communication of  2 PM8000, 1 slave and 1 master as image below.

 

How do i do in PM8000? Thanks very much

 

This is my configure in PM8000. Do i it right or wrong?

 

Image 0: Architecture 

TH1.png

 

Image 1: Config PM8000 is Master

 

PM8000 Master_TH1.JPG

 

 

Image 2: Config PM8000 is Slave

 

PM8000 Slave_TH2 vs TH1.JPG

 


Accepted Solutions
Charles_Murison
Picard Picard
Picard
0 Likes
1
1834

Re: Config communication PM8000

rest of the settings look good.

L4 Prime for Advanced metering and Utilities

See Answer In Context

Charles_Murison
Picard Picard
Picard
0 Likes
6
1812

Re: Config communication PM8000

The PM8000 has 2 different ways to be a gateway

Ethergate: 

Ethernet connected meter, Com Protocol: Ethergate 

Connect to the meter on port 7801, only 1 connection at a time. Can be either ION or Modbus, depends on the setting of RS485 meter and the software connecting to the meter. Recommended only 1 protocol on the RS-485 loop, not recommended mix ION and mosbus.

 

Modbus gateway:

Ethernet connected meter,

Com Protocol: Modbus Master   

Modbus master option module, Serial connection 1 -> Comm1  Gateway enabled and serial connection 1 selected

RS-485 Meter com protocol has to be Modbus.

Multiple connections to the gateway meter possible on port 502. One big downside is that the RS-475 meter does not have access to logged values, waveforms etc when using Modbus.

 

If using PME to talk to the RS-485 meter. STRONGLY recommend using ethergate, as no default drive to talk modbus to the PM8000 in PME.

 

L4 Prime for Advanced metering and Utilities

See Answer In Context

SESA_B
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
2
1783

Re: Config communication PM8000

Hi @Yut ,

 

Because my customer hard supply IP. So, we just need 01 PM8000 is Ethergate, 08 PM8000 will slave with modbus RS485

 

Hic.

See Answer In Context

Charles_Murison
Picard Picard
Picard
0 Likes
1
1761

Re: Config communication PM8000

Modbus master is used 1 for 2 possible conditions, 1, the meter is modbus mastering the slave devices itself, or 2, the meter is acting as a modbus gateway only, no other protocol is able to talk to downstream devices. Many features of the PM8000 meter are only avalaiable to the ION Protocol especially when using PME so I DO NOT recommend using modbus for the downstream device.

 

Ethergate is able to transfer the ION requests from Ethernet to serial and then back to ethernet to PME. Port 7801 is only used with Ethergate and the meter can only use 1 setting for the serial side. You will still only use 1 IP address but it will be duel function, 1 device is an ethernet device, the downstream device is a serial device on ethernet gateway.

L4 Prime for Advanced metering and Utilities

See Answer In Context

Yut
Captain
Captain
0 Likes
1
1748

Re: Config communication PM8000

You can use the first PM8000 as gateway using ION protocol.

See Answer In Context

19 Replies 19
Charles_Murison
Picard Picard
Picard
0 Likes
5
1853

Re: Config communication PM8000

Com 1 Serial port between the 2 meters do not match, Master is 8E2, slave is 8N1. Both need to match.

L4 Prime for Advanced metering and Utilities
SESA_B
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
4
1850

Re: Config communication PM8000

Hi Charles,

 

Thanks you. I will revise.

 

I will configure as follows:

 

 - PM8000 is master:

                                  + COM1 Protocol: EtherGate

                                  + COM 1 Baud rate: 9600

                                  + COM1 Timeout: 3.000

                                  + COM1: Unit ID: 1

                                  + COM1: Serial port: 8E2

                                  + COM1: RS485 Bias: ON

 

- PM8000 is Slave:   

                                  + COM1 Protocol: ION

                                  + COM 1 Baud rate: 9600

                                  + COM1 Timeout: 3.000

                                  + COM1: Unit ID: 3

                                  + COM1: Serial port: 8E2

                                  + COM1: RS485 Bias: ON

 

Is the configure correct?

 

 

 

Charles_Murison
Picard Picard
Picard
0 Likes
3
1846

Re: Config communication PM8000

Hello,

 

If you can do faster than 9600 baud rate without communications issues I would suggest that 19.2k is pretty common. On the slave meter I would disable the RS485 Bias.

L4 Prime for Advanced metering and Utilities
SESA_B
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
2
1841

Re: Config communication PM8000

Hi Charles,

 

Yes. Thanks Charles. I know and i also want use Baud rate 19,2k. But, My customer PME system use 9200 because their system unstable.

 

I will disable RS485 bias at slave meter.

 

And the rest in this setting it ok? Thanks Charles

Charles_Murison
Picard Picard
Picard
0 Likes
1
1835

Re: Config communication PM8000

rest of the settings look good.

L4 Prime for Advanced metering and Utilities
Robert_Lee
Captain Captain
Captain
0 Likes
8
1832

Re: Config communication PM8000

Question I have is the PM8000 the only slave device on the RS-485?  If there are other Modbus device on the same loop, you will likely need to reconfigure the protocols and move to Modbus Gateway which uses Modbus Master (instead of Ethergate) on the gateway PM8000 and Modbus RTU (instead of ION) on the slave PM8000.  You would also need to set the Modbus Gateway to COM1 via ION Setup (Basic Ethernet -> TCP/IP tab).  You will also need recent PM8000 firmware and PME in order to support ION over Modbus in order to operate in this manner.  We do not recommend mixing ION devices using ION protocol with Modbus-based devices on the same RS-485.

If there are only ION meters on the RS-485, then what you have shown is correct (although your original diagram Image 0: Architecture indicated Modbus protocol and not ION).

 

Also you will be restricted to a single master (PME by the looks of it) to communicate to the slave PM8000 (i.e. trying to use another application like ION Setup will result it in not able to connect to the Ethergate port of 7801 while PME is connected).

SESA_B
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
7
1816

Re: Config communication PM8000

Hi Robert,

 

Thanks you. Yes. The only PM8000 slave device in loop RS485.

 

So, my architecture is correct?. My customer only read value fundamential: I, V, P, E.

 

Thanks Robert.

 

SESA_B
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
0
1814

Re: Config communication PM8000

Hi Charles,

 

Thanks for your support. 

Charles_Murison
Picard Picard
Picard
0 Likes
6
1813

Re: Config communication PM8000

The PM8000 has 2 different ways to be a gateway

Ethergate: 

Ethernet connected meter, Com Protocol: Ethergate 

Connect to the meter on port 7801, only 1 connection at a time. Can be either ION or Modbus, depends on the setting of RS485 meter and the software connecting to the meter. Recommended only 1 protocol on the RS-485 loop, not recommended mix ION and mosbus.

 

Modbus gateway:

Ethernet connected meter,

Com Protocol: Modbus Master   

Modbus master option module, Serial connection 1 -> Comm1  Gateway enabled and serial connection 1 selected

RS-485 Meter com protocol has to be Modbus.

Multiple connections to the gateway meter possible on port 502. One big downside is that the RS-475 meter does not have access to logged values, waveforms etc when using Modbus.

 

If using PME to talk to the RS-485 meter. STRONGLY recommend using ethergate, as no default drive to talk modbus to the PM8000 in PME.

 

L4 Prime for Advanced metering and Utilities
SESA_B
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
0
1802

Re: Config communication PM8000

Hi Charles,

 

Thanks Charles.

Yut
Captain
Captain
0 Likes
3
1790

Re: Config communication PM8000

Why MODBUS you can get most of PM8000 with PME using ION Protocol ?

SESA_B
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
2
1784

Re: Config communication PM8000

Hi @Yut ,

 

Because my customer hard supply IP. So, we just need 01 PM8000 is Ethergate, 08 PM8000 will slave with modbus RS485

 

Hic.

SESA_B
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
4
1774

Re: Config communication PM8000

Hi @Charles_Murison @Yut ,

 

I was configure for the first PM8000 is Master (Modbus master) and the second PM8000 is slave look like image below.

 

Settinng for masterSettinng for masterSetting for SlaveSetting for SlaveSetting in PMESetting in PME

But when i configure in PME. I can't reveive data. Pls see and recommend for me if i wrong setting.

 

Thanks very much

Charles_Murison
Picard Picard
Picard
0 Likes
3
1768

Re: Config communication PM8000

On the  PM8000 is Master, change the port 1 protocol to Ethergate.

L4 Prime for Advanced metering and Utilities
SESA_B
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
2
1766

Re: Config communication PM8000

Hi @Charles_Murison ,

 

Thanks for your information. But why PM8000 port 1 replace from Modbus Master to Ethernet Gateway?

Charles_Murison
Picard Picard
Picard
0 Likes
1
1762

Re: Config communication PM8000

Modbus master is used 1 for 2 possible conditions, 1, the meter is modbus mastering the slave devices itself, or 2, the meter is acting as a modbus gateway only, no other protocol is able to talk to downstream devices. Many features of the PM8000 meter are only avalaiable to the ION Protocol especially when using PME so I DO NOT recommend using modbus for the downstream device.

 

Ethergate is able to transfer the ION requests from Ethernet to serial and then back to ethernet to PME. Port 7801 is only used with Ethergate and the meter can only use 1 setting for the serial side. You will still only use 1 IP address but it will be duel function, 1 device is an ethernet device, the downstream device is a serial device on ethernet gateway.

L4 Prime for Advanced metering and Utilities
SESA_B
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
0
1755

Re: Config communication PM8000

Hi @Charles_Murison ,

 

Sincerely, Thanks for your information. I'm smootly hehe.

 

 

Yut
Captain
Captain
0 Likes
1
1749

Re: Config communication PM8000

You can use the first PM8000 as gateway using ION protocol.

SESA_B
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
0
1735

Re: Config communication PM8000

Hi @Yut ,

 

Thanks very much.