Clock synchronization problems

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Clock synchronization problems
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All
Related Products
product field
Schneider Electric
PowerLogic ION9000
product field
PowerLogic
PowerLogic ION8650 series

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Ricardo_RM
Lieutenant JG Ricardo_RM
Lieutenant JG

Posted: ‎2024-02-05 08:42 AM

0 Likes
5
1549
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-02-05 08:42 AM

Clock synchronization problems

Hello community

A customer has a problem with the PME's time synchronization with the meters.

 

He mentions that the problem is in all the meters that are integrated into the PME.

An example that he mentions to us is that of an ION9000, where it is 3 seconds late, but has not synchronized for 9 days (the client does this synchronization manually). As seen in the following image:

 

Ricardo_RM_1-1707150608634.png

 


Another example that he mentions is the following one that takes 2 minutes of difference, as seen in the image:

 

Ricardo_RM_2-1707150657087.png

 

 

They have synchronization activated, as seen in the image:

 

Ricardo_RM_3-1707150702718.png

 

 

Thus, with all the meters, the list of firmware they have is additionally presented, where you can see what happens with the meters with updated firmware and those that do not have it.

 

Ricardo_RM_4-1707151088067.png

 

 

That's why we wanted to know if you have any idea what may be going on.

 

Thank you so much..

 

  • Thumbnail of PowerLogic ION9000
    Schneider Electric
    PowerLogic ION9000
  • Thumbnail of PowerLogic ION8650 series
    PowerLogic
    PowerLogic ION8650 series
View products (2)
Labels
  • Labels:
  • ION7000
  • ION8000
  • ION9000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
Captain

Posted: ‎2024-02-07 12:34 PM

0 Likes
0
1483
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-02-07 12:34 PM

Hi @Ricardo_RM 

As Charles mentioned previously, there is an option in meter's Security Option Module named:
'Allow Broadcast Timesyncs' which can be checked in Advanced mode of ION Setup:

Mehran_0-1707334097290.png

and defines whether or not a username and password must be supplied to synchronize the time of the device (when advanced security is enabled).

If set to NO, it indicates that a username and password must always be supplied by any software used to synchronize the device time. In this case, the checkbox in PME -> MC -> Meter Security Settings needs to be checked.

If it is set to YES, then time synchronization can be performed without a username and password, then there is no need to check that checkbox.

 

Best Regards,

-Mehran

Expert Technical Support Specialist

See Answer In Context

Reply
Replies 5
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-02-05 09:10 AM

0 Likes
3
1545
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-02-05 09:10 AM

Hello @Ricardo_RM ,

The settings in PME is just step 1. The second is what are the settings inside the meter including security. One item to note, the clock module was set to line frequency, in general if syncing the meter more than once a month I would not recommend using this setting. Internal is a better option.

Is PME set to broadcast time sync or to send authenticated packet? Is meter setup with advanced security? Is broadcast time sync allowed? 

Are you able to capture traffic to/from the meter? Either inside the switch connected to the meter or possibly having the switch do a port mirror to another port where you can monitor the traffic with a computer running Wireshark?

regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Ricardo_RM
Lieutenant JG Ricardo_RM
Lieutenant JG

Posted: ‎2024-02-06 11:59 AM

0 Likes
2
1509
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-02-06 11:59 AM

Hello @Charles_Murison 

 

Thank you very much for the response, one question, where can you see that the PME is configured to transmit time synchronization or send authenticated packets?

 

And what is the difference between them?

 

The other questions are asked to the client.

 

thank you so much

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-02-06 04:10 PM

0 Likes
1
1503
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-02-06 04:10 PM

Hello @Ricardo_RM ,

To  see if PME will use authenticated time sync packets, go to device in management console -> right click device -> security. Check box as shown below will give the status. I am not 100% sure if this info is also possible in web device manager or not.

Charles_Murison_0-1707264456624.png

The difference is the time sync packet can either have no authentication information (broadcast) or user and password specific information as found in the security section of Mangement console (again pictured above).

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Ricardo_RM
Lieutenant JG Ricardo_RM
Lieutenant JG

Posted: ‎2024-02-07 05:27 AM

0 Likes
0
1499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-02-07 05:27 AM

Hello @Charles_Murison 

 

Thank you so much

 

What would be recommended, is the option shown in the image active or not?

 

Regards,

Reply
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
Captain

Posted: ‎2024-02-07 12:34 PM

0 Likes
0
1484
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-02-07 12:34 PM

Hi @Ricardo_RM 

As Charles mentioned previously, there is an option in meter's Security Option Module named:
'Allow Broadcast Timesyncs' which can be checked in Advanced mode of ION Setup:

Mehran_0-1707334097290.png

and defines whether or not a username and password must be supplied to synchronize the time of the device (when advanced security is enabled).

If set to NO, it indicates that a username and password must always be supplied by any software used to synchronize the device time. In this case, the checkbox in PME -> MC -> Meter Security Settings needs to be checked.

If it is set to YES, then time synchronization can be performed without a username and password, then there is no need to check that checkbox.

 

Best Regards,

-Mehran

Expert Technical Support Specialist

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of