Hello,
Does the ION9000 or PM8000 have the ability to log synchrophasor data per IEEE c37.118?
The AESO now requires this data for load shedding contracts with it's customers. Have seen on competitor products I would consider entry-level PQ metering, but cannot find any info on whether our meters support it.
Regards,
– Scott Clysdale
Link copied. Please paste this link to share this article on your social media post.
No. Neither the ION9000 nor PM8000 measure synchrophasor data per IEEE c37.118.
Can you share the exact AESO requirement you are referring to?
I don't think I have found the particular requirement you are referring to (new requirement for load shed contracts) on the AESO website... but I do see a revision in progress for Section 502.9 that describes some requirements for a PMU (Phasor Measurement Unit) when applicable. Hopefully the new updates will clarify requirements using the newer editions of IEEE c37.118.1a-2014 and IEEE c37.118.2-2011. (Or the newer IEEE 60255-118-1-2018)
Dan
Link copied. Please paste this link to share this article on your social media post.
No. Neither the ION9000 nor PM8000 measure synchrophasor data per IEEE c37.118.
Can you share the exact AESO requirement you are referring to?
I don't think I have found the particular requirement you are referring to (new requirement for load shed contracts) on the AESO website... but I do see a revision in progress for Section 502.9 that describes some requirements for a PMU (Phasor Measurement Unit) when applicable. Hopefully the new updates will clarify requirements using the newer editions of IEEE c37.118.1a-2014 and IEEE c37.118.2-2011. (Or the newer IEEE 60255-118-1-2018)
Dan
Posted: 2021-05-19 08:15 AM
Link copied. Please paste this link to share this article on your social media post.
Hi Dan,
From the customer (Alberta Pacific):
"Currently the AESO requires us to achieve the IEEE C37.118-2005 Class 1. Now there is also a 2011 addendum to that standard with P and M classes that would also be acceptable, and may be required at some point in the future (but are not currently)."
Checking back with ALPAC to find the AESO requirement doc for you.
Regards,
– Scott
Posted: 2021-05-19 09:50 AM
Link copied. Please paste this link to share this article on your social media post.
Hi Dan,
Here's the AESO standard: https://www.dropbox.com/s/ww3vjhyufx1u81u/502.9-Synchrophasor-Measurement-Unit-Technical-Requirement...
From the customer:
"Any new facilities since 2013 are also bound by 502.9 (see attached), which lists the IEEE standard mentioned (see highlighted portion).
In addition our LSSI contract stipulates a minimum rate of 30 measurements per second which puts us in the class 1."
Let me know if this info helps!
Regards,
– Scott
Link copied. Please paste this link to share this article on your social media post.
Hello,
Following up this topic, does the latest ION8650 or ION9000 utility meter support IEEE c37.118 standard?
https://standards.ieee.org/ieee/C37.118.1/4902/
Thanks
Leo
Link copied. Please paste this link to share this article on your social media post.
Hello @Liangchen1982 ,
Answer is still no.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @Charles_Murison ,
Quick follow-up, is there a roadmap to add support for measuring synchrophasor data per IEEE c37.118?
Thank you,
Jeremy
Link copied. Please paste this link to share this article on your social media post.
Hello @jeko88 ,
I have not heard anything about this. I would suggest working with the sales team to create a feature request. If you can provide the sales team with a estimated number of units to be sold, this would be helpful.
Regards,
Charles