I have some daisy-chains of Digitrip 810D's that are currently communicating via PowerLogic (Sy/Max) protocol to PME. These are communicating via various gateways (EGX100, EGX200, LINK150, etc.). I understand that the last gateway to communicate PowerLogic protocol is the LINK150 that is due to be discontinued. It is also the last to have 4-wire RS-485 support. Can I use the PM8000/ION9000 4-wire module (METSEPMRS4854W) as a gateway for the downstream Digitrip 810D's? What communication settings should I use in the PM8000 if this is possible? Thank you in advance for your assistance.
Link copied. Please paste this link to share this article on your social media post.
Hello @sesa77040_bridg ,
The PM8000/ION9000 4-wire module (METSEPMRS4854W) does not support PowerLogic (Sy/Max).
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @sesa77040_bridg ,
The PM8000/ION9000 4-wire module (METSEPMRS4854W) does not support PowerLogic (Sy/Max).
Regards,
Charles