Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PM8000 ring topology RSTP

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8000 ring topology RSTP
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
NicoleTang
NicoleTang Contributor
Contributor

Posted: ‎2023-10-18 03:38 PM

0 Likes
1
1880
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-10-18 03:38 PM

PM8000 ring topology RSTP

Hi everyone.

I have read few forums in here in regards to RSTP or ring topology on PM8000 meters.

I am still not sure from the forums whether RSTP has been implemented successfully on site.

I have a site that has just been upgraded to Cisco managed switches, and we have PM8000 meters on site that are daisy-chained in a ring, back to the switch (to occupy 2 ports).

There are 3 loops, and one loop consists of 4 PM8000 meters, another of 5, and another of 10 PM8000.

The meters are connected to just the dedicated VLAN and the meters RSTP are enabled also.

First 2 loops of 4 and 5 PM8000s were connected as a ring without issue. The last loop of 10 PM8000 caused a network wide shutdown. 

I want to know if there is:

1. a limit or number of PM8000 that can be daisy chained in a ring

2. a prefer or specific RSTP or STP protocol to use that works with PM8000

3. maybe firmware fix released? The meters are by the customer and I noticed they varied in firmware from the menus

 

Appreciate technical advice. Thanks.

Attachments
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2023-10-19 09:02 AM . Last Modified: ‎2023-10-19 09:03 AM

1 Like
0
1868
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-10-19 09:02 AM

Hello @NicoleTang ,

 

1. a limit or number of PM8000 that can be daisy chained in a ring
CM: There is more of a performance limitation rather than protocol limitation. As you increase the number of devices, the amount of time for network to settle when there is a change takes longer.

2. a prefer or specific RSTP or STP protocol to use that works with PM8000
CM: RSTP is the protocol PM8000 meters support. 

3. maybe firmware fix released? The meters are by the customer and I noticed they varied in firmware from the menus
CM: There were changes to RSTP on the meters around the V2.2.0 time range. If you meter is V3.0.0 or newer firmware should not be a factor.

Be sure the meters and switches have RSTP enabled before connecting the meters in a loop. If loop is made before RSTP is enabled, the network will see a storm of traffic and likely have networks not happy.

 

Regards,

Charles

 

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Reply 1
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2023-10-19 09:02 AM . Last Modified: ‎2023-10-19 09:03 AM

1 Like
0
1868
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-10-19 09:02 AM

Hello @NicoleTang ,

 

1. a limit or number of PM8000 that can be daisy chained in a ring
CM: There is more of a performance limitation rather than protocol limitation. As you increase the number of devices, the amount of time for network to settle when there is a change takes longer.

2. a prefer or specific RSTP or STP protocol to use that works with PM8000
CM: RSTP is the protocol PM8000 meters support. 

3. maybe firmware fix released? The meters are by the customer and I noticed they varied in firmware from the menus
CM: There were changes to RSTP on the meters around the V2.2.0 time range. If you meter is V3.0.0 or newer firmware should not be a factor.

Be sure the meters and switches have RSTP enabled before connecting the meters in a loop. If loop is made before RSTP is enabled, the network will see a storm of traffic and likely have networks not happy.

 

Regards,

Charles

 

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.